a little more...
(dc ckts) Neutral is midpoint between a positive and a negative. Relative to ground, the potential differnce is usually zero, but that is not necessarily true. In power electronics, it may be true only on average, such as in some switched-mode power supplies where the neutral voltage bounces above and below zero, but is zero on average.
Ground is generally 'earth' or equipment frame or chassis or building iron or a ground rod driven into the ground, and is usually associated with the human safety side of the electrical system. Neutral and ground may be directly connected, or may be connected with an intentional impedance between them (search on 'high resistance grounding'). For these circuits, under normal conditions there is no potential difference between neutral and ground.
The key is what happens when there is a fault, where part of the live circuit gets connected to the frame. If left unchnaged, there is a shock hazard. By having the frame electrically connected between its own parts and bonded to the grounding circuit ensures a current path to the power supply, which then ensures the fault protective system (e.g. circuit breaker) recognizes the problem (such as sudden high current) and disconnects the circuit. A resitance between neutral and ground can be used to detect current even when low, hence still sense a fault.
I hope this helps.