Difference in material between 1250A, 40KA & 1250A, 50KA?

  • Thread starter Thread starter moh abdelsalam
  • Start date Start date
  • Tags Tags
    Difference Material
AI Thread Summary
The discussion focuses on the differences in materials used for 1250A, 40KA and 1250A, 50KA busbars at medium voltage (10.5KV). Key considerations include the choice of conductor materials, with aluminum alloys being common but presenting challenges in mechanical and electrical connections. The design must account for electrical characteristics and structural integrity, particularly under high current fault conditions, which can cause conductors to attract and potentially touch. Increased fault current ratings necessitate more robust support structures, raising overall costs for busbars and breakers. The use of current limiting inductors in switchgear is also mentioned as a strategy to manage fault currents and reduce expenses.
moh abdelsalam
Messages
2
Reaction score
0
At M.V. (10.5KV), what is the difference in material between 1250A, 40KA busbar & 1250A, 50KA?
 
Engineering news on Phys.org
hi and welcome to PF :smile:

your question is extremely vague
What material ?
outline more clearly what you are referring to with as much relevant info as possible :smile:
 
  • Like
Likes moh abdelsalam
davenn said:
hi and welcome to PF :smile:

your question is extremely vague
What material ?
outline more clearly what you are referring to with as much relevant info as possible :smile:
I'm sorry, I'm talking about busbar material (the conductor, insulation, supports and etc...).
 
Last edited:
Here's some busbar information. This seems to be for more typical busbars and may not be as useful for high power applications. Still, most of the same problems will still need to be solved.

For high power AC systems, lots of engineering work will need to be done. The electrical characteristics will depend on geometry. Typically these will be large hollow roundish metal structures. Aluminum alloys are a popular choice, but has some concerns about mechanical/electrical connections.

After the electrical characteristics are determined, structural problems need to be solved.

This is a specialized field and you may need to hire a power engineer with experience with station/substation design if you need specifics.
 
  • Like
Likes moh abdelsalam
One of the design considerations is rigidity.
Under high current faults the conductors are attracted to one another,
wirefor.gif
so it is required they be stout enough that a downstream fault will not make them bend and touch between supports which would cause another fault.

So i'll assume your 40 and 50 ka numbers are fault current ratings,beyond the 1.25 ka.
Presumably the busbar is supported as necessary and made more rigid considering the forces produced by fault current. Those forces are in proportion to the product of the currents as indicated in that Hyperphysics image above, http://hyperphysics.phy-astr.gsu.edu/hbase/magnetic/wirfor.html

502/402 = 1.56+,
ie 56% more bracing required.

That of course raises the cost of busbar and breakers.

Sometimes you'll see a current limiting inductor in switchgear.
It limits fault current allowing use of less expensive busbar and breakers downstream . My plant had them in the 4kv switchgear , located between the breakers supplying multi-thousand horsepower motors and those feeding only multi-hundred horsepower motors.
 
  • Like
Likes davenn and FOIWATER
Very basic question. Consider a 3-terminal device with terminals say A,B,C. Kirchhoff Current Law (KCL) and Kirchhoff Voltage Law (KVL) establish two relationships between the 3 currents entering the terminals and the 3 terminal's voltage pairs respectively. So we have 2 equations in 6 unknowns. To proceed further we need two more (independent) equations in order to solve the circuit the 3-terminal device is connected to (basically one treats such a device as an unbalanced two-port...
suppose you have two capacitors with a 0.1 Farad value and 12 VDC rating. label these as A and B. label the terminals of each as 1 and 2. you also have a voltmeter with a 40 volt linear range for DC. you also have a 9 volt DC power supply fed by mains. you charge each capacitor to 9 volts with terminal 1 being - (negative) and terminal 2 being + (positive). you connect the voltmeter to terminal A2 and to terminal B1. does it read any voltage? can - of one capacitor discharge + of the...