Physics_Kid
- 172
- 11
i have some test data, 1sec while i run the equation using my test #'s
You're trying to be too precise.Physics_Kid said:the k value i gave earlier in post # 23 is wrong, the R=10 is per 2" so i need to multiply by 12 to get it into 1ft terms, so R=120
ok, so here's a test i ran earlier using some electrical wire with THWN insulation. it was 14awg. the PVC insulation has a very thin layer of nylon over the top.
the nylon is ~10x thinner than the PVC
PVC k=0.19
nylon k=0.25
so net conductivity k = ~0.17W/mK = 0.0982btu/ft hr oF
wait while i finish here
The units in each term of the equations have to be consistent with each other, so the final units are temperature. What is the equation for k in terms of the R value?Physics_Kid said:yes, 14awg @26amps had a ΔT of 28oF, ambient air was 56oF, but the TC probe i am using is a metal tube (i think its stainless) and 0.1"dia x 2.5" long, the probe was wrapped with some insulation but the metal was heatsinking it, etc. this test was free air test of 14awg with THWN insulation on it.
the equations you gave, should k be in terms of feet, or the actual k value for the thickness of the insulation? notice i used R=10 for 2", that's R=60 for 1ft.
The thermal conductivity is related to R by ##k=\frac{δ}{R}##, where δ is the thickness of the insulation (in our case 2"). When working with R values, you need to know whether R is given in US units or SI units. The two are not equivalent. If R is in US units, its units are ##\frac{hr-ft^2-F}{BTU}##. Which is it for the insulation you are using, US or SI units?Physics_Kid said:R=1/k
but it was not clear to me if we needed actual R of the insulation thickness, or R per ft. it sounds like we need 1/R per ft of insulating material. this is quite different than the std Q=AΔT/R equation because this basic equation uses actual R value of the dimensions used, not a normalized R value, etc.
i was getting to the calculation of pvc coated wire, 1sec
Something looks wrong with this calculation.Physics_Kid said:14awg with THHN insulation @26amps (1ft)
i am using k value for the insulation
1 W/(m K) = 1 W/(m oC) = 0.85984 kcal/(h m oC) = 0.5779 Btu/(ft h oF) = 0.048 Btu/(in h oF)
and http://www.engineeringtoolbox.com/thermal-conductivity-d_429.html
does not show k using area
ri = 2.7x10-3ft
ro = 4.4x10-3ft
h =1btu/ft2-hr-oF
T0 = 55oF
Qwire = 262*0.00259=1.75W=1.75J/s=6303J/hr=6.303kJ/hr , 1kJ=0.9478btu, =5.97btu/hr-ft
kinsulation = 0.0982btu/ft-hr-oF, approx R=10.1 = 1/k
Tw=55 + 5.97/6.28*0.0982 * ln(4.4/2.7) + 5.97/6.28*4.4x10-3*1
Tw=55 + 9.68 * 0.488 + 216.1
Tw=55 + 4.7 + 216.1
Tw= 275.8oF
not even close to what my test has shown. with some error i think my wire is around 90oF[/SUP]
OK. What about the 4.4 E-3, and the 2.7 E-3?Physics_Kid said:before was 12awg @10amps
the later is 14awg @26amps
I have no idea what you're talking about, but shouldn't that 4.7E-3 be 2" = 0.167 ft.Physics_Kid said:those are the dimensions of 14awg with THWN insulation on it.
before was 12awg @10amps with hypo 2" radius insulation that had R=5/inch, the non-SI R value
the later is 14awg @26amps with real thickness of THWN insulation, measured with my digital caliper, the nylon coating is about 10x thinner than the pvc under it.
Are you saying that the wire is not embedded between two sheets of 2" thick insulation in the second example?Physics_Kid said:so, in the 1st scenario we said 12awg with a radial insulator of 2" radius, length = 1ft, this to simplify the equations for a exothermic wire in a tubular insulator.
in my test data i used real 14awg wire from romex cable, the insulation on the wire is rather thin, no where near 2" radius. the insulation is made up of a layer of pvc and then coated in nylon. the nylon layer is approx 10x thinner than the pvc layer. this scenario is really no different than the 1st except for amps, dimensions of the wire, and insulator thermal conductivity.
the last term in your equation is very strong compared to the others. a little Q and the term is rather large. ~2watts and the term is in the 200's
A value of h equal to 8 - 10 is not atypical either. It looks like this would be a more accurate choice, given your data. Try a value of 8 and see what you get. But, if this is correct, the outside of the insulated wire should be warm to the touch. Was it?Physics_Kid said:i have not yet ran any sandwich testing. the 14awg test is wire in open air, simply some 14awg copper surrounded by tubular insulator.
Yes. Exactly. There are air currents in the room from the ventilation (so-called forced convection) and also natural convection resulting from the buoyancy effect of the insulation surface being at a different temperature than the room air. What we've done here is use your experimental data to calibrate the model (i.e., get an estimate of the value of h). This result tells us that, with the actual 2" of insulation in place, this term will have a much smaller effect than the heat conduction through the insulation in terms of influencing the wire temperature.Physics_Kid said:at ~90F measured, yes, it was a light warm to the touch
h=8 does then get real close to measured, including some error for the metal TC probe
i measured 83F, equation with h=8 says 86.7F, which is in alignment with some heatsink affect from the metal TC probe.why a change in h ? is it something that swings that much depending on the environment of air to convect heat away from the wire?
Exactly right again. You're on a roll.in this specific calculation, the #'s i used, the wire was 84" long, ran this test with a "long" wire thinking the heatsink affect at the ends would be very insignificant. but now i am interested to see how you factor in heatsinks on the ends of the wire. i suspect the factor will be a minus to the existing equation.
What I think is that you are trying to get too exact at this stage. If, after we're done with the sink effect, you want a more accurate estimate of the relation between the heat flow and the temperature difference (which properly takes into account the effects of this geometry), we can solve the 2D heat transfer problem either analytically or numerically.Physics_Kid said:hi Chet,
so with a flat rectangular sandwich what we end up with (looking at the end where the wire exits) an infinite # of radii from centerline to the insulation surface. its a simple triangle with a short side ro-min and a long side ro-max
to use this annular equation do you think it is ok to approximate the rectangular sandwich using 2* ro-min ?
for a 24"x4" sandwich = 962in
Acirc=6.28 r2
r=3.9
which is ~ 2*ro-min
cant use 2x as a general rule, would just solve for r of a circle having equivalent area of the rectangle.
your thoughts?
Physics_Kid said:hi Chet,
yes, ready to see heat transfer term for the heat sinks.
Cu conductivity is 401W/m⋅K
the contact pad between the Cuwire and clamp is approx 2mm2
the clamp is steel (low carbon) and has conductivity of 43W/m⋅K
the clamp is in free air and has area Aclamp
there's actually a tad more than that going on because the clamp is holding the copper to the power supply lug ends, which are lugs connected to 2awg insulated copper stranded wire. but for this problem i don't think we need to worry about it.
i might conclude that the shiny nylon jacket with black pvc underneath has h between 8-10 as you said. h=8 seems to fit my test data rather well.
Surface coefficient
Approximate surface heat transfer coefficients that are reasonable accurate for low temperature surfaces in still air ( which are the conditions experienced for insulated systems are listed below)
h = 5.7 for low emissivity surfaces such as polished aluminium
h = 8.0 for surfaces of medium emissivity - galvanised steel , aluminium paint, stainless steel etc
h = 10 for surfaces of high emissivity - matt black surfaces, brick and plain insulated surfaces.