Conducting an Earth Resistivity Test on a concrete-covered property presents challenges, particularly with probe placement for the Fall-of-Potential method. Using an existing earthing rod as one of the probes is a potential solution, but the length of the probe can affect resistivity calculations. For those unable to access the ground due to concrete, measuring external loop impedance (Ze) live with a multifunction tester is recommended. It is crucial to connect the tester correctly to avoid introducing parallel paths that could skew results. The need for accurate earth resistivity readings is emphasized due to local authority audit requirements and equipment safety verification.
Forum Researcher
Messages
2
Reaction score
0
TL;DR Summary
I am planning to conduct an Earth Resistivity Test on my property. The issue is that my building's basement is entirely covered with concrete and pavement, and we intended to use the Fall-of-Potential test method since there are no other equipment options available for rent in my location. However, I am unable to place the probes wherever I need to take the readings.
Hi, I am planning to conduct an Earth Resistivity Test on my property. The issue is that my building's basement is entirely covered with concrete and pavement, and we intended to use the Fall-of-Potential test method since there are no other equipment options available for rent in my location. However, I am unable to place the probes wherever I need to take the readings. Therefore, I have a few questions:

  • Is it possible to use the other earthing rod/pit as one of the probes?
  • Does the length of the probe matter? If yes, what changes may require in calculation of resistivity?
  • Is there an alternative method to perform the test without expensive equipment?
  • What are the best practices for situations like these?
 
Engineering news on Phys.org
Welcome to PF.
Why do you want to measure earth resistivity?
 
  • Like
Likes Forum Researcher
Normal method is to use two spikes and a multifunction tester:
IMG_1159.jpeg


However, if there’s concrete in the way, the best way is to measure the external loop impedance (Ze) live using the same device. That is, the loop from transformer line, through the tester, through the earth/ground path, and back to the transformer. The tester is connected between line and ONLY the earthing rod, not to the earth bar as this will introduce parallel paths via water/gas pipes etc.

I would ask, gently, that if you don’t know this, or haven’t got the test gear, should you be commissioning a supply?
 
Baluncore said:
Welcome to PF.
Why do you want to measure earth resistivity?
I am required to submit the earth resistivity test reports as part of the local authority's annual audit; if I don't, I will be fined.
Setting audit aside, I need to inspect the ground points in order to verify the safety of the expensive equipment as well.
 
The L distance in the diagram above is typically 30-50m. Wouldn’t that take you outside the building to some soil where you can push in the test stakes?
 
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...