Efficiency of a synchronous machine.

AI Thread Summary
The discussion focuses on calculating the power and efficiency of a delta-configured synchronous machine with given parameters, including armature resistance, open circuit voltage, and short circuit current. The participant has calculated the synchronous impedance (Zs) as 200 ohms and synchronous reactance (Xs) as 198.5 ohms but is uncertain about the equivalent circuit values needed for power calculations. Clarification is sought regarding whether the armature resistance and reactance values should be adjusted due to the delta configuration. It is confirmed that these values remain unchanged in a delta setup. The participant is looking for further assistance to proceed with the calculations.
Sharples049
Messages
3
Reaction score
0

Homework Statement


The armature resistance per phase is given as 24.7ohms.
Delta configured machine.
Open circuit voltage is 220v, short circuit current is 1.1A at 3000rpm.
Rpm is dropped to 1500rpm and no load line voltage is 100.
Find power and efficiency if an inductive load of 1.4H is applied at the load.

Homework Equations


As per synchronous machines electrical theory.

The Attempt at a Solution


Still working on it but simulation results aren't the same. Any help will be appreciated thankyou.
 
Physics news on Phys.org
You need to show your attempt. You can start by calculating the synchronous impedance (Zs) from OC and SC data given.
 
cnh1995 said:
You need to show your attempt. You can start by calculating the synchronous impedance (Zs) from OC and SC data given.
Hi, thanks for your reply.
ok so far i have Zs to be 200ohms from the OC and SC data. By substituting the armature resistance to find the synchronous reactance Xs, I have Xs to be 198.5ohms. This is where I'm becomming stuck, it is a delta configured machine so I'm unsure of what the equivalent circuit values will be in order to calculate power.
 
Since this is delta configuration, VL=Vph=100V.
 
cnh1995 said:
Since this is delta configuration, VL=Vph=100V.
I'm stuck after that mate. Haven't done much on synchronous machines. Will the equivalent circuit be made up of the 24.7ohms and inductance calculated from Xs, then the load? Or will the Ra and Xs values be different due to the delta formation?
Any help will be much appreciated.
 
upload_2016-1-30_17-16-6.jpeg

The values will not change in delta. You can use them as they are.
 