Harmonic sources, flowing from load, why?

AI Thread Summary
Nonlinear loads can be viewed as harmonic current sources because they generate harmonic currents that flow back into the grid, particularly when passive filters are employed to mitigate specific harmonics. This phenomenon occurs because the load current is influenced by the characteristics of the load itself rather than solely the source, leading to a non-sinusoidal current waveform. When a passive filter is connected, it can absorb these harmonics, allowing the supply to only need to provide the fundamental current. The terminology of "injecting" or "withdrawing" harmonics can be misleading, as it depends on the perspective of the observer. Understanding this interaction requires recognizing that circuits can be analyzed from either a voltage or current perspective, affecting how we interpret the flow of harmonics in the system.
OliskaP
Messages
38
Reaction score
7
I have been thinking of this and can not seem to understand why nonlinear loads can be tought of harmonic current sources injecting current back into the grid?

For example if you connect a passive filter in parallel to attenuate the 5th harmonic, the 5th harmonic would flow between the filter and the load, and the supply do not need to supply 5th harmonic current.

I can not seem to understand why? How can the load produce harmonic currents? I have always been thinking that current flows from the source to the load, but then again its AC the current flows back and forth all the time.

Still, I can not figure out why non linear loads can be tought of current sources injecting into the grid instead of drawing harmonic current from the source.Best regards
 
Engineering news on Phys.org
The more accurate word would be "causing" harmonic currents. Injecting or withdrawing are more like a glass half full or half empty, the depend on the speaker's point of view.

The words we chose in natural language are not always the most scientifically accurate ones.
 
  • Like
Likes OliskaP
This is a good use for LT Spice - considering a rectifier (diode or thyristor) only conduct when the device is forward biased, so current only flows when the line voltage is higher than the DC voltage. -- Look at the waveform images part way down this page. The load current is controlled by the load, not the source - and it is not a sine wave of current.

You will typically add a line reactor to attenuate this first -as the reactor will inhibit the rapid current rise and fall as the diodes "turn on " and off.

From the grid perspective - the term injected is misleading(but is is just a term), however the various inductive elements in the grid have to react to this load current. The impact is seen from the LOAD back towards the source.
 
  • Like
Likes OliskaP
Thanks for the explanations @anorlunda and @Windadct , but I am still abit confused when a passive shunt filter is connected in parallel, see figure.

So if a nonlinear load causes flow of fundamental + harmonics, but the filter is implemented in such a way that the source only has to supply fundamental. This is confusing to me, unless we can think of:

1. The nonlinear load to "inject" harmonics back into the grid, and the filter is present to absorb it, so that the supply only have to provide fundamental current.
OR
2. The filter providing the harmonic currents to the load, thus again the supply only has to supply fundamental current.
Capture.JPG
 
Both 1 and 2 sound equivalent to me. Feel free to choose either.
 
Realizing that the shunt filter is effectively a "short" to current above some frequency ( 5th of 60 = 300 Hz) ... I think part of the issue is we typically prefer to see think of circuits from a voltage source perspective, but in reality any circuit can be seen from a voltage or current thinking.

If you were to look at the current for each of the 4 branches - coming into the node they would each be different. The filter would ONLY have current above some frequency and Ideally, look like an open ckt to 60 (50) Hz - in Voltage or Current. The Non-linear load has Fundamental and High Harmonic current, the source can accept the harmonics but has a higher impedance than the filter, so the harmonics to the source are reduced but not eliminated.
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
Thread 'Beauty of old electrical and measuring things, etc.'
Even as a kid, I saw beauty in old devices. That made me want to understand how they worked. I had lots of old things that I keep and now reviving. Old things need to work to see the beauty. Here's what I've done so far. Two views of the gadgets shelves and my small work space: Here's a close up look at the meters, gauges and other measuring things: This is what I think of as surface-mount electrical components and wiring. The components are very old and shows how...

Similar threads

Replies
3
Views
2K
Replies
2
Views
2K
Replies
13
Views
3K
Replies
9
Views
2K
Replies
4
Views
2K
Replies
2
Views
1K
Replies
10
Views
2K
Back
Top