Heat exchange in active system

AI Thread Summary
To cool water in a 200-liter tank by 10 degrees Celsius using a coiled copper pipe, calculations indicate that 125 kW of power must be extracted from the incoming hot water at 50 degrees Celsius. The required flow rate of cold water to achieve this cooling is approximately 1.2 liters per second, assuming the tank maintains an average temperature of 45 degrees Celsius. The thermal conductivity of the copper coil suggests minimal temperature drop across the pipe wall, ensuring efficient heat transfer. The size of the tank primarily affects the time it takes to reach the desired temperature rather than the cooling efficiency itself. Exploring variable adjustments could enhance the overall system's efficiency and performance.
paullom
Messages
2
Reaction score
0
I am trying to calculate the amount of water that would have to pass through a 200 litre tank (water inlet temp is 20degrees c) in order to cool water by 10degrees in a closed loop (in a coiled copper pipe) suspended in the tank the coil has a total length of 30 lineal m and a diametre of 20mm the water in the coil enters at 50 degrees and is traveling at approximately 3 litres per second. I am a geologist not a physician and this has me stumpt. Any help or advise would be much appreciated.
 
Science news on Phys.org
It’s been a while since I did these sorts of sums but..

For the temperature in the tank to be constant the power entering must match that extracted so first work out the power in Watts (=Joules/second) entering the tank via the hot coil using:

Heat capacity of water = 4180 J/Kg/K
Temperature drop (10 K)
Mass of water per second (3kg/S)

= 4180 * 10 * 3
= 125,400 J/S
= 125 kW

So that's how much has to be removed by the cold water flow.

Quick check that the coil is big enough. Last time I did this I used this equation:

Dt = (P * Wt)/(A * C)

Where

Dt = average delta T across wall of pipe in Centigrade
C = thermal conductivity of copper = 401 W•m−1•K−1
Wt = wall thickness in meters? Assume 2mm = 0.002m ?
A = area of pipe wall in meters = Pi * 0,02 * 30 = 1.88sqm
P = Power in watts

Dt=(125*10^3 * 0.002)/(1.88 * 401)
=0.33K

So can assume no temperature drop across wall of copper pipe (unless it scales up!)

Incoming hot is 50C, require 10C drop so it leaves at 40C. Average 45C

Lets assume water temperature of the tank is maintained at 45C.

Temperature rise of cooling water is 45-20C = 25C

Flow rate required is

= 125,400/(4180 * 25)
= 1.2L/Sec

Note that it will come out colder than required until the tank is upto temperature. that might take quite awhile.
 
Thanks a lot for that.
It all make sense to me and is far simpler than I thought. I think I will play with the variables to see if I can improve the effeciency and size etc of the system. I am using this to try and build a ground water cooled refrigerant system.

Re the calc for the suitability of the coil length if i change the parameters at what point do you think that the temperature drop across the pipe is of any concern to the whole system?

Does the size of the tank have any bearing on any of this, or is it as I suspect that it will only vary the time it takes for the tank to reach the average water temp.

Again thanks a bunch.
 
I need to calculate the amount of water condensed from a DX cooling coil per hour given the size of the expansion coil (the total condensing surface area), the incoming air temperature, the amount of air flow from the fan, the BTU capacity of the compressor and the incoming air humidity. There are lots of condenser calculators around but they all need the air flow and incoming and outgoing humidity and then give a total volume of condensed water but I need more than that. The size of the...
Thread 'Why work is PdV and not (P+dP)dV in an isothermal process?'
Let's say we have a cylinder of volume V1 with a frictionless movable piston and some gas trapped inside with pressure P1 and temperature T1. On top of the piston lay some small pebbles that add weight and essentially create the pressure P1. Also the system is inside a reservoir of water that keeps its temperature constant at T1. The system is in equilibrium at V1, P1, T1. Now let's say i put another very small pebble on top of the piston (0,00001kg) and after some seconds the system...