Heat exchanger capacity (condenser and evaporator)

AI Thread Summary
To determine heat exchanger capacity in a window-type air conditioner, focus on measuring changes in the refrigerant rather than the air. The most accurate method involves using the mass flow rate of the refrigerant and its change in enthalpy to calculate heat absorption. While specific heat can be used for dry air, moist air requires additional considerations for condensed water. The pressure increase from a fan is minimal, typically around 1 kPa. Accurate data collection is essential for reliable results in experiments related to heat exchangers.
plucker_08
Messages
54
Reaction score
0
Window-type Aircon

how to get this in an actual experiment?

is it just (mass flow rate of the refrigerant X specific heat X Change in temp of the refrigerant)

or (mass flow rate of the air passing thru the heat exchanger X specific heat X Change in temp of the air)

or (mass flow rate of the refrigerant X change in enthalpy (outlet and inlet state of the refrigerant)

or (mass flow rate of the air X Change in enthalpy of the air)
 
Engineering news on Phys.org
First, think about what control volume you are doing the analysis on. Are you measuring the air or the refrigerant? Under ideal situations, the heat absorbed by the refrigerant is the same as the heat rejected in the room. But practically, you are much more likely to get good data measuring changes in the refrigerant.

This eliminates your second and fourth equations.

Your first equation assumes that the refrigerant is a perfect gas but because in a traditional vapor-compression refrigeration cycle the flow through a heat exchanger is typically two-phase this is a bad assumption, hence this equation does not apply.

Your third equation will allow you to properly calculate the amount of heat absorbed.
 
The first response is fine, but just a quick fyi - if the air is dry, you can use the specific heat times delta-T times mass flow for the air, but if it is moist, you'll need to add the specific heat and mass flow of condensed water. But just using enthalpy instead covers that.

Btw, there is a recent thread about a window heat pump unit where I do this exact experiment. I'm trying to get a paper published.
 
can i use the pyschrometric chart for 100KPa, even if the air is blown thru fan?

the air pressure increases when blown by fan, right?
 
Yes, air pressure increases when blown through a fan, but not by much. A powerful air conditioning fan might give you 1kPa of pressure rise.
 
Posted June 2024 - 15 years after starting this class. I have learned a whole lot. To get to the short course on making your stock car, late model, hobby stock E-mod handle, look at the index below. Read all posts on Roll Center, Jacking effect and Why does car drive straight to the wall when I gas it? Also read You really have two race cars. This will cover 90% of problems you have. Simply put, the car pushes going in and is loose coming out. You do not have enuff downforce on the right...
I'm trying to decide what size and type of galvanized steel I need for 2 cantilever extensions. The cantilever is 5 ft. The space between the two cantilever arms is a 17 ft Gap the center 7 ft of the 17 ft Gap we'll need to Bear approximately 17,000 lb spread evenly from the front of the cantilever to the back of the cantilever over 5 ft. I will put support beams across these cantilever arms to support the load evenly
Thread 'What's the most likely cause for this carbon seal crack?'
We have a molded carbon graphite seal that is used in an inline axial piston, variable displacement hydraulic pump. One of our customers reported that, when using the “A” parts in the past, they only needed to replace them due to normal wear. However, after switching to our parts, the replacement cycle seems to be much shorter due to “broken” or “cracked” failures. This issue was identified after hydraulic fluid leakage was observed. According to their records, the same problem has occurred...
Back
Top