How Do Steam Plants Use Different Fuels?

  • Thread starter Thread starter Delta Force
  • Start date Start date
  • Tags Tags
    Plants Steam
AI Thread Summary
Steam plants historically adapted to different fuels, transitioning from coal to petroleum and later to natural gas due to economic factors and energy crises. Modifications for fuel conversion include adding appropriate burners, adjusting air fans, and re-calibrating control systems. Coal-to-oil conversions are more complex due to the physical space required for burning coal, necessitating the removal of coal handling equipment. Some facilities, particularly in areas like NYC, must operate dual fuel systems for flexibility in fuel use. Understanding these adaptations is crucial for optimizing steam plant operations and ensuring safety and efficiency.
Delta Force
Messages
81
Reaction score
7
Historically it wasn't uncommon for boilers to be run on fuels different from those they were originally designed for. Ships were commonly converted from coal to petroleum after the 1910s, and for a period of time it was common to convert power plants from coal to petroleum as well. A common feature then and now is the use of petroleum to help start coal fired power plants or improve their burning of coal. After the energy crises of the 1970s and the increased cost of petroleum many power plants were converted to coal, including some that were originally designed to burn petroleum. Some steam plants were built to run on natural gas as well.

I haven't been able to find a diagram of anything other than a coal fired steam plant and I haven't been able to find any information on what exactly is done to change a power plant between fuel types. Does anyone know what kind of modifications are done to allow the different fuel types to be burned? Are there any diagrams of steam plants in different configurations?
 
Engineering news on Phys.org
Oil to gas is easy; you just change the burner. It's basically just a flamethrower that bolts over a hole at the bottom of the boiler.

Coal to oil would be more complicated because of how much space a burning bed of coal takes up.
 
I can't say that I've seen conversion project plans, but I think I can outline the steps.

  1. Add fuel handling to bring the fuel to the furnace. Coal pulverizers can be eliminated.
  2. Add burners of appropriate size (this is what @russ_watters mentioned. (By the way, coal is blown into the furnaces as a fine dust, not burned in beds.) Also, igniters need to be appropriate.
  3. Each burner must be dynamically adjustable to match the original proportions of heat to furnace/superheater/reheater sections.
  4. Weld shut the wet bottom of the furnace (where coal slag was removed).
  5. Adjust the primary and secondary air fans to provide enough air without wasting fan power.
  6. Remove/bypass the bag house and precipitators from the exhaust end used to catch flyash from coal.
  7. Re-calibrate and re-tune the boiler control systems.
  8. Re-design safety and startup/shutdown logic.
  9. Evaluate safety contingencies.
  10. Re-program the training simulator (if any) and retrain the operators.
In some cases, like in the NYC area, they are required to fuel with oil or gas with rapid switching between fuels. That means dual fuel systems.

Edit: add re-design control room panels.
 
  • Like
Likes jim hardy
russ_watters said:
Coal to oil would be more complicated because of how much space a burning bed of coal takes up.
anorlunda said:
In some cases, like in the NYC area, they are required to fuel with oil or gas with rapid switching between fuels. That means dual fuel systems.
And coal requires pulverizers and fans to blow the dust into the boiler. Totally different fuel handling than oil or gas which are pumped in pipes right to their respective burners.

Our fossil units burned oil or natural gas (when we could get it) or a mix. We didn't have coal in Florida.
The analog pneumatic control system controlled the flows of both fuels into the burners, and positions of dampers inside the boiler. Gas with its blue flame has less radiant heat than oil's yellow-orange flame so the gas gets routed a little differently through the superheaters.. .[/QUOTE]
 
Posted June 2024 - 15 years after starting this class. I have learned a whole lot. To get to the short course on making your stock car, late model, hobby stock E-mod handle, look at the index below. Read all posts on Roll Center, Jacking effect and Why does car drive straight to the wall when I gas it? Also read You really have two race cars. This will cover 90% of problems you have. Simply put, the car pushes going in and is loose coming out. You do not have enuff downforce on the right...
I'm trying to decide what size and type of galvanized steel I need for 2 cantilever extensions. The cantilever is 5 ft. The space between the two cantilever arms is a 17 ft Gap the center 7 ft of the 17 ft Gap we'll need to Bear approximately 17,000 lb spread evenly from the front of the cantilever to the back of the cantilever over 5 ft. I will put support beams across these cantilever arms to support the load evenly
Thread 'What's the most likely cause for this carbon seal crack?'
We have a molded carbon graphite seal that is used in an inline axial piston, variable displacement hydraulic pump. One of our customers reported that, when using the “A” parts in the past, they only needed to replace them due to normal wear. However, after switching to our parts, the replacement cycle seems to be much shorter due to “broken” or “cracked” failures. This issue was identified after hydraulic fluid leakage was observed. According to their records, the same problem has occurred...

Similar threads

Back
Top