greydient said:
I guess I'm still a little rusty (and therefore confused). I have my m-dot, but this is how the fluid flow changes with time, not the energy.
M is mass. You calculate the energy by using the equation I gave.
And I don't have p for my system - just e in Watts.
Watts is power, not energy. Energy is watt-hours.
For example, if you have a 1kW heating element and 100kg of water circulating through your system, the heating element dissipates 1kWh of energy per hour.
c for water is 4.186 J/g*C and a Joule is a watt-second, so...
1000*3600/4.186/100,000= 8.6 degrees C/hr.
FYI, the question itself contains an error (which is probably why you were confused!), which is what led the others astray. Since it is a closed system, flow rate is irrelevant, only total mass matters.
Also, as others noted, there are other complexities here. I ignored them because we have no information about them, but if your pump is big enough it will add a noticeable amount of heat to the system and unless the system is perfectly insulated, it will lose heat as you add heat.
Btw, I occasionally use the above procedure to manually size the heating element on a water heater/heating system. Water heater volume is based on usage and heating element is based on a "recovery rate", usually taking a full tank of cold water up to operating temperature in about an hour.