How much energy to heat a room, and heat pump efficiency?

AI Thread Summary
To heat a 10 ft. x 10 ft. room, approximately 1000 watts of power is needed, based on a requirement of 10 watts per square foot. This translates to 1 kWh to maintain a typical temperature. A heat pump operating in a cooler climate can achieve a coefficient of performance (COP) of 2.5, meaning it requires less input power. The discussion clarifies that "watts per hour" is incorrect terminology; it should be referred to as watt-hours. Additionally, 1000 watts is equivalent to about 3413 BTU per hour when discussing heating power.
ProtoBob
Messages
6
Reaction score
0
O.K. this is maybe a large question...

I am trying to find out how much energy it would take to do the work of a heat pump compressor that would be required to heat a... let's say 10 ft. x 10 ft. room of a typical house.

I know there are a lot of variable here...

What I am trying to discern from this, is, if there were an alternate method to drive a heat pump compressor motor, how much energy would be required to do so...

Any thoughts?
 
Science news on Phys.org
You're not looking for energy, you are looking for power. This is very dependent on things like insulation and climate. A good starting guess of required heating for a relatively cool climate (say, the northeastern United States) would be 10 W/sq ft. A decent heat pump has a COP of 2.5 when it is cold outside, so that gives an input power of 4 W/sq ft.
 
If I am understanding correctly, that's 10 watts per sq. ft. so a 10 x 10 room would be
100 sq. ft. requiring 100 * 10 watts, or 1000 watts to maintain a "typical" temperature.

Could this also be stated as 1000 watts per hour or 1kwh to maintain room temperature?

would this also be equivalent to 3413 btu per hour?

Thanks! :)
 
ProtoBob said:
If I am understanding correctly, that's 10 watts per sq. ft. so a 10 x 10 room would be
100 sq. ft. requiring 100 * 10 watts, or 1000 watts to maintain a "typical" temperature.
Could this also be stated as 1000 watts per hour or 1kwh to maintain room temperature? [/quote] There is no such thing as "watts per hour". There is watts for an hour, which is watt-hours (or 1000 watt-hours = 1 kWh). Watts is already a rate.
would this also be equivalent to 3413 btu per hour?
Yes, though note that people do a kind of short-hand and often interchange "BTU" and "BTUH". BTU is technically the rate (power, like kW) and BTUH is the energy (like kWh).
 
I was watching a Khan Academy video on entropy called: Reconciling thermodynamic and state definitions of entropy. So in the video it says: Let's say I have a container. And in that container, I have gas particles and they're bouncing around like gas particles tend to do, creating some pressure on the container of a certain volume. And let's say I have n particles. Now, each of these particles could be in x different states. Now, if each of them can be in x different states, how many total...
Thread 'Why work is PdV and not (P+dP)dV in an isothermal process?'
Let's say we have a cylinder of volume V1 with a frictionless movable piston and some gas trapped inside with pressure P1 and temperature T1. On top of the piston lay some small pebbles that add weight and essentially create the pressure P1. Also the system is inside a reservoir of water that keeps its temperature constant at T1. The system is in equilibrium at V1, P1, T1. Now let's say i put another very small pebble on top of the piston (0,00001kg) and after some seconds the system...