- 23,695
- 11,137
- TL;DR Summary
- HVAC unit is throwing an over/under voltage fault. 24V transformer reads 26V. How do I get it down to 24V?
My friend bought a condo last winter and now in cooling season her AC unit (water source heat pump) is faulting-off sporadically. I've done some basic troubleshooting, and the unit is showing a over/under voltage fault on its LED. It's a 208V/1ph unit. According to the manual, the controller reads the control voltage and figures if it's out of range that means the primary voltage is out of range. Control voltage is 24VAC nominal and the alarm limits say 18-31.5V. In non-coincident measurements, I found the line voltage to be 208V on the dot and control 25.6V. That doesn't seem like it's far off, and is within tolerance. But the problem seems to occur more often at night, when I'd expect the line voltage to un-sag and go up some. Old building, old city - I bet it varies quite a bit with load and I just happened to measure it when it was exactly right.
I was going to leave this to a service tech, but I'm having trouble finding one to service a WSHP. And the more I look at this, the more it seems it may be a simple fix. In reading-up on little transformers, I see it is common for them to have a low-load voltage significantly above nominal and then just let them sag. So I'm thinking about three potential options:
1. Replace the control transformer.
2. Add a resistor in series to drop the control voltage.
3. Switch the control transformer tap from 208 to 240V to drop the control voltage to about 22.2V.
For #1, the transformer is cheap and looks easy to replace. But if it's common to have a real voltage above the nominal I may just end up with the same problem. For #2, the resistance depends on the load, right? It's a 50 VA transformer, but is likely not using anywhere near that much. I calculate that if it's using 20 VA then a 2.6 ohm resistor would drop about 2V. Is it really that simple or am I missing something? Risks?
It's a ClimateMaster CXM controller. Several PDFs on the issue at the top of the google search HERE. There's a bit of conflicting info on the fault; it says 10% tolerance, but the actual voltage range given is more like 30%. The existing transformer is a pretty standard multi-tap HVAC control transformer, except that it's 50 VA and most I see when googling are 40. It does appear to be wired properly for its voltage.
If need be I can install a voltage logger on her incoming power service to find out what the voltage is really doing over time. For example, since yesterday my household voltage has been varying between 120V in the day and 125V at night.
Other thoughts?
Other thoughts?