How to use flow rates (GPM) and pressure drop to determine if a valve is usefull

AI Thread Summary
To determine if the Burkert model 457361D valve can handle a flow rate of 50 GPM, the Cv value of 35.1 is crucial, as it indicates flow capacity at a 1 psi pressure drop. The flow must be turbulent for the standard equation Cv = Q √(SG/ΔP) to be valid, with turbulent flow occurring at a Reynolds number of 10,000. The ISA standard S75.01.01 provides detailed guidelines for calculating flow and pressure drop, emphasizing the importance of avoiding choking conditions. Users should consult the valve manufacturer for specific sizing information to ensure accurate assessments. Understanding these principles is essential for effective valve selection and performance evaluation.
MoonKnight
Messages
6
Reaction score
0
I need to determine if a valve can handle a flow rate of 50 GPM, this valve being: 2/2 Way, Normally closed, w/ 2-pilot control, and coupled solenoid.

I also need to determine pressure drop...

it is a burkhert model - 457361D

the valve specs indicate:

Cv = 35.1

pressure measurement = 0 -145 psi


if anyone can help, or push me in the right direction, thanks...
 
Physics news on Phys.org
The Cv is your main source of information. The Cv is, by definition, the amount of flow through the valve with a delta P across it of 1 psi. Most valve suppliers will give you a curve of Cv vs. % open. You can use the following equation to calculate the flow through given the following equation:

Cv = Q \sqrt{\frac{SG}{\Delta P}}
 
The equation given is generally correct as long as there is no choking, and the flow is laminar.

The ISA standard S75.01.01 gives extensive information on the subject. Also, the valve manufacturer should provide sizing information that will take that into account.

www.ostand.com
 
ooops I meant to say the flow must be TURBULENT.
 
proinwv said:
The equation given is generally correct as long as there is no choking, and the flow is laminar.

The ISA standard S75.01.01 gives extensive information on the subject. Also, the valve manufacturer should provide sizing information that will take that into account.

www.ostand.com

proinwv said:
ooops I meant to say the flow must be TURBULENT.

I've never heard of a restriction on the flow being turbulent for that equation to be valid. Where did you reference that from?

CS
 
It is part of the ISA S75.01.01 This is "the" standard of the valve industry.

Most references ignore this at their peril. Choking occurs when the pressure in the vena contracta within the valve drops to the vapor pressure of the liquid and vaporization occurs, preventing further flow increases, unless the inlet pressure is increased.

Turbulent flow rather than laminar or transitional will pass the amount indicated by the equation that was quoted earlier. Otherwise the equation must be modified by a valve reynolds number factor which is =<1. Turbulent flow occurs when the valve reynolds number is 10,000. This is calculated by the equations in the ISA standard.

If these factors are not checked for signifcant errors can occur in the calculation of flow or delta p.
 
This might be of some use in understanding what I was trying to say, as it relates to turbulent flow.
 

Attachments

thanks for your help guys... I found what I needed a while ago, but your responses were appreciated
 