In a small hydropower plant, the operation of asynchronous generators differs significantly from synchronous generators, particularly in frequency and active power control. Asynchronous generators require reactive power to function, complicating their use in islanded mode, as they typically need external excitation. However, techniques such as using a doubly fed induction generator or integrating a large DC capacitance in the converter can enable operation in islanded mode. The torque-speed curve illustrates the relationship between electrical frequency and rotor speed, emphasizing the importance of reactive power management for voltage stability. Overall, while using asynchronous generators presents challenges, effective control strategies can facilitate their integration into hydropower systems.
vampslayer
Messages
24
Reaction score
0
Let's say we have small hydropower plant which can operate in on-grid and in islanded mode too.
I understand a principles of frequency and active power control in a case we have synchronous generator, but what would be diff in a case of Asynchronous generator? How do we controll frequency in a case of A.G?

Since the Asynchronous generator needs reactive power to work, how can hydropower plant with Asynchronous generator work in ISLANDED mode then?
 
Engineering news on Phys.org
It can't, with the most common type of asynchronous generator, the plain old induction machine.. You must provide such a generator with exciting power to its stator.

Remember that an induction machine will be a generator if it's spun > synchronous speed
and it will be a motor if it's spun < synchronous speed.
The speed-torque curve is symmetrical about synchronous speed.

With no external voltage there's nothing for it to be synchronous with, or asynchronous either.

Perhaps it'd be better to call the two types of machine by their other names, "Wound Rotor" and Induction".
 
Hello Vamp- and sorry Jim... I must disagree with "It can't", this is used in wind generation frequently, and known as doubly fed induction generator. ( https://en.wikipedia.org/wiki/Doubly_fed_electric_machine )

However in islanded mode - this would take some tricks in the controls - but should be possible, I am thinking a rather large DC Capacitance in the converter.

Of course Asynchronus can also mean a PM Generator - just not in sync, that can be handled by a power converter. ( Rectify then Inverter to pure AC) - for a smaller power system, this would be the way to go due to efficiency. Up to 100KW or so this is often referred to as micro-hydro.
 
No disagreement here. I should have said 'it's not nearly so straightforward as with a synchronous machine'


Here's a link to a pretty good paper I stumbled across a while back
https://www.calvin.edu/~pribeiro/courses/Power%20Systems%20Interim/wind-generator-types.pdf

with generic generator descriptions...
 
Thx both of you
 
The below is related to a squirrel-cage IM in island mode:

If you draw the torque-speed curve for motor and generator operation, you will notice how the slip changes according to loading (active power). This gives a direct correlation between the electrical frequency and the rotor speed.

As for reactive power, which is closely related to voltage, is also depends on the active and reactive loading of the generator. A fixed capacitor bank connected to the terminals of the machine provides reactive power in relation to the voltage squared. Increasing the reactive power loading decreases the voltage, which could have a severe effect on the system. In order to increase the voltage, more capacitor must be switched in. A SVC (static VAR compensator) or STATCOM could control the reactive power in a "step-less" manner.

Small portable generators may have a simple IM with fixed capacitor bank, and voltage is in such system may vary to a large extent.
 
Thread 'Weird near-field phenomenon I get in my EM simulation'
I recently made a basic simulation of wire antennas and I am not sure if the near field in my simulation is modeled correctly. One of the things that worry me is the fact that sometimes I see in my simulation "movements" in the near field that seems to be faster than the speed of wave propagation I defined (the speed of light in the simulation). Specifically I see "nodes" of low amplitude in the E field that are quickly "emitted" from the antenna and then slow down as they approach the far...
Very basic question. Consider a 3-terminal device with terminals say A,B,C. Kirchhoff Current Law (KCL) and Kirchhoff Voltage Law (KVL) establish two relationships between the 3 currents entering the terminals and the 3 terminal's voltage pairs respectively. So we have 2 equations in 6 unknowns. To proceed further we need two more (independent) equations in order to solve the circuit the 3-terminal device is connected to (basically one treats such a device as an unbalanced two-port...