I have questions about circuit breakers .

Click For Summary
SUMMARY

This discussion focuses on the testing and specifications of Oil and Air Circuit Breakers. The dielectric strength of Oil Circuit Breakers is assessed using type 10-C transformer oil, which should have a dielectric capability greater than 35 kV for fresh oil and no less than 15 kV for used oil. The UL 489 standard governs the testing of Air Circuit Breakers, requiring them to pass overload and short-circuit tests, with a minimum short-circuit test of 5000A. These circuit breakers are essential for electrical distribution panels, ensuring safety and reliability in electrical systems.

PREREQUISITES
  • Understanding of dielectric strength testing for insulating oils
  • Familiarity with UL 489 standards for circuit breakers
  • Knowledge of electrical distribution systems and circuit protection
  • Basic principles of thermal conductivity and capacity in insulating materials
NEXT STEPS
  • Research dielectric strength testing methods for transformer oils
  • Study the UL 489 standard in detail for circuit breaker compliance
  • Explore the principles of short-circuit testing in electrical devices
  • Investigate the characteristics and applications of type 10-C transformer oil
USEFUL FOR

Electrical engineers, circuit breaker manufacturers, and professionals involved in electrical safety and compliance testing will benefit from this discussion.

strangecomer
Messages
2
Reaction score
0
Welcome everybody in this forum.

I would like to ask about Oil circuit breaker, there is a dielectric strength test of its oil so, I want any documents about that, containing the voltage that the oil will breakdown in it , accents of oil that has been broken down and the name plate of the oil circuit breaker.

And,I want any documents about Air circuit breaker tests:
-instantaneous trip test.
-Time delay trip test.

and the name plate of Air circuit breaker.

Please answer me ,thanks.

Regards
 
Engineering news on Phys.org
there is no answer, I still waiting.

regards
 
1-The type of oil that has been used in virtually all oil circuit breakers is one where naphthenic base petroleum oils have been carefully refined to avoid sludge or corrosion that may be produced by sulfur or other contaminants.
The resulting insulating oil is identified as type 10-C transformer oil. It is characterized by an excellent dielectric strength, by a good thermal conductivity (2.7 x l0-4 cal/sec cm ˚C) and by a high thermal capacity (0.44 cal/gm ˚C).
The purity of the oil usually can be judged by its clarity and transparency. Fresh oil has a clear amber color, while contaminated oil is darkened and there are some black deposits that show signs of carbonization. The condition of the oil normally is evaluated by testing for its withstanding capability. The tests are made using a spherical spark gap with two spheres 20 mm in diameter and at a gap of 3 mm.
Fresh oil should have a dielectric capability greater than 35 kV. For used oil it is generally recommended that this capability be no less than 15 kV.

2-UL 489 encompasses circuit breakers “intended for installation in a circuit breaker enclosure or as parts of other devices, such as service entrance equipment and panel boards.” According to UL terminology, devices meeting this standard are considered listed products.
For approval, UL 489 requires the device pass a series of calibration, overload, endurance and short-circuit tests. The minimum short-circuit test must be performed at 5000A. Overload tests are performed at six times the current rating of the device or 150A minimum. Devices rated up to 600V and
6,000A are covered in this standard. Additionally, most UL 489 devices are used in electrical distribution panels; therefore, the minimum current ratings available are seldom less than 15A. During UL 489 testing, the device must survive short-circuit testing and continue to provide future overload protection.
In service entrance panels, available short-circuit fault currents measure 50,000A or greater. However, as power is distributed throughout a building, the available short-circuit currents diminish. If an electrical outlet is just 20 feet away from the power source, Ohm’s law states even with limitless available short-circuit current AWG 14 copper wire limits the maximum available fault current at the outlet to no more than 1200A at 120V.



-----------------------------------------------------------------
Creative thinking is enjoyable, Then think about your surrounding things and other thought products. http://electrical-riddles.com
 

Similar threads

  • · Replies 23 ·
Replies
23
Views
4K
  • · Replies 8 ·
Replies
8
Views
3K
  • · Replies 5 ·
Replies
5
Views
6K
  • · Replies 19 ·
Replies
19
Views
2K
  • · Replies 2 ·
Replies
2
Views
27K
Replies
53
Views
5K
  • · Replies 3 ·
Replies
3
Views
3K
  • · Replies 7 ·
Replies
7
Views
6K
  • · Replies 32 ·
2
Replies
32
Views
4K
  • · Replies 32 ·
2
Replies
32
Views
4K