Is Multiplying Phase Readings a Valid Method to Verify Transformer Load Balance?

AI Thread Summary
Multiplying phase readings to verify transformer load balance is questioned, as it may not accurately confirm the correctness of the readings or the neutral current. Neutral current can arise from both unbalanced loads and third harmonic currents, particularly from older electronic devices. To effectively analyze neutral current, using a spectrum analyzer is recommended to differentiate between line frequency unbalance and harmonic contributions. This method provides a clearer understanding of the actual load conditions. Accurate assessment of transformer load balance requires careful consideration of these factors.
Muhammad Saber
Messages
1
Reaction score
0
I'm working in electrical company in a department in which I receive transformer LV side ampere readings and in most of these readings the neutral has amperege due to unbalanced loading, all I need a method in which I be certain that these readings are actual measured values specially neutral measuremen to make reldistributing the load to the phases, I thought that when I multiply the r,s,t readings the phase between r,s,t which is 120 diffrence it will make me be sure that these phases reading are correct and the neutral amperege. Is that right , if not what is the way to investigate these readings.
 
Engineering news on Phys.org
Muhammad Saber said:
I thought that when I multiply the r,s,t readings the phase between r,s,t which is 120 diffrence it will make me be sure that these phases reading are correct

i cannot make sense of that sentence.

What are you multiplying by what ? and why ?


Muhammad Saber said:
and the neutral amperege
Neutral current includes both unbalance AND third harmonic current.
Electronic devices made before power factor correction was mandated draw a lot of third harmonic current that shows up in the neutral. .
You'll need to look at your neutral current with a spectrum analyzer to know how much of it is at line frequency(unbalance) and how much is at 3X line frequency(electronic loads).
 
Last edited:
  • Like
Likes dlgoff
Thread 'Weird near-field phenomenon I get in my EM simulation'
I recently made a basic simulation of wire antennas and I am not sure if the near field in my simulation is modeled correctly. One of the things that worry me is the fact that sometimes I see in my simulation "movements" in the near field that seems to be faster than the speed of wave propagation I defined (the speed of light in the simulation). Specifically I see "nodes" of low amplitude in the E field that are quickly "emitted" from the antenna and then slow down as they approach the far...
Hello dear reader, a brief introduction: Some 4 years ago someone started developing health related issues, apparently due to exposure to RF & ELF related frequencies and/or fields (Magnetic). This is currently becoming known as EHS. (Electromagnetic hypersensitivity is a claimed sensitivity to electromagnetic fields, to which adverse symptoms are attributed.) She experiences a deep burning sensation throughout her entire body, leaving her in pain and exhausted after a pulse has occurred...