Japan Earthquake: Nuclear Plants at Fukushima Daiichi

Click For Summary
The Fukushima Daiichi nuclear plant is facing significant challenges following the earthquake, with reports indicating that reactor pressure has reached dangerous levels, potentially 2.1 times capacity. TEPCO has lost control of pressure at a second unit, raising concerns about safety and management accountability. The reactor is currently off but continues to produce decay heat, necessitating cooling to prevent a meltdown. There are conflicting reports about an explosion, with indications that it may have originated from a buildup of hydrogen around the containment vessel. The situation remains serious, and TEPCO plans to flood the containment vessel with seawater as a cooling measure.
  • #12,841
westfield said:
A note to all related to that - the FHM's across the 6 units at fukuichi are not even close to identical.

Though, if I may moderate your expression, the FHM's of unit 2, unit 3, and the common pool, all do appear to be very similar.
 
Engineering news on Phys.org
  • #12,843
MadderDoc said:
But on top of that, moments after the explosion we have this big cloud rising over the building, apparently approximately spherical, 75 m diameter -- which would be a volume of about 220000 m3. So where did this huge volume of air come from, how did it get there, what was its composition??

As the steam plumes on the right-after-the-explosion picture suggests the containment integrity was broken at that time. As I recall after the explosion the RPV remained on ambient pressure.

So my bet:
The PCV released pressure and the hydrogen stocked up in the secondary containment till it exploded: this was the first 'bang'.

Then the RPV damaged and the overheated water in it turned to steam. This steam (and some more hydrogen) built the big cloud. Fortunately the wind moved the cloud toward the ocean, so the site remained relatively safe: also the steam separator stopped the worst of the solid fuel debris.
 
  • #12,844
For general reference, here are a couple of images and a couple of videos that represent the most recent views of the reactor buildings that I have been able to find so far:

These photos are from March 11th 2012 I believe:

http://msnbcmedia.msn.com/j/reuters/2012-04-03t131611z_1_cbre83210v200_rtroptp_3_japan-tsunami.grid-6x3.jpg

http://msnbcmedia.msn.com/i/reuters/2012-03-30t130143z_1_cbre82t106y00_rtroptp_3_japan-tsunami.jpg

This video is from late Feb when they reduced the flight exclusion radius:



This video has a few seconds that appear more recent, starting from the 33 second mark of this youtube clip:



I note that the met viable signs of progress at reactor 3 are the removal of damaged building at ground level to the north of the reactor, and the construction of a structure near the north-east of the reactor building.
 
Last edited by a moderator:
  • #12,845
westfield said:
That ladder IS strange to be just there but I don't think we can be so conclusive about how it remained there and how the FHM got where it is..

For instance it's not impossible that the ladder could have jammed itself in that position in the FHM floor track as the FHM went into the pool, only later to have the roof truss come down next to it, ladder has nowhere to go as its stuck in the track so it's handrail "clips" itself over the roof truss section.

Not a bad idea, though I don't get how or why the hand rail 'clips' itself over the truss. Seems like that 'clip over' effect might be best explained by a downward pull as the FHM falls into the pool, briefly deforming the rail downward (clip down) before the relatively weak rail snapped.

In any scenario how that truss gets in there is really bizarre. If it did so before the FHM fell, was it thrust at an almost horizontal angle like a javelin? That seems very unlikely. I'm also not sure based on the before photo if there was enough room for it to slide under the rail. Very strange indeed!
 
  • #12,846
  • #12,847
Rive said:
As the steam plumes on the right-after-the-explosion picture suggests the containment integrity was broken at that time. As I recall after the explosion the RPV remained on ambient pressure.

So my bet:
The PCV released pressure and the hydrogen stocked up in the secondary containment till it exploded: this was the first 'bang'.

Then the RPV damaged and the overheated water in it turned to steam. This steam (and some more hydrogen) built the big cloud. Fortunately the wind moved the cloud toward the ocean, so the site remained relatively safe: also the steam separator stopped the worst of the solid fuel debris.

That isn't consistent with pressure data (March 14th):

Code:
Time                    RP(A)   RP(B/C) D/W       S/C      FNT    BHT     WL(A)  WL(B)   DW R/H         Ref
                        MPa abs MPa abs MPa abs   MPa abs  gr.C   gr.C    meter  meter   gr.C

23:00, March 14th       N/A     0.297   0.370     dscale    N/A    N/A     N/A   -2.30
22:40, March 14th       N/A     0.290   0.360     dscale    N/A    N/A     N/A   -2.30
22:00, March 14th       --approximate time for a fire at unit 3 or 4 -----------------
21:04, March 14th       N/A     0.270   0.360     dscale    N/A    N/A     N/A   -2.30
20:03, March 14th       N/A     0.284   0.360     dscale    N/A    N/A     N/A   -2.30
19:30, March 14th       N/A     0.283   0.335     0.500     N/A    N/A    -1.90  -2.30
19:00, March 14th       N/A     0.284   0.360     dscale    N/A    N/A     N/A   -2.30
17:00, March 14th       N/A     0.362   0.440     0.440     N/A    N/A     N/A   -2.20
16:00. March 14th       - webcam shows smoke coming from unit 3-----------------------
16:00, March 14th       N/A     0.409   0.480     0.475     N/A    N/A     N/A   -2.20
15:00, March 14th       N/A     0.399   0.480     0.470     N/A    N/A     N/A   -2.20
14:00, March 14th       N/A     0.382   0.460     0.450     N/A    N/A     N/A   -2.20
13:00, March 14th       N/A     0.352   0.430     0.430     N/A    N/A     N/A   -2.20
12:00, March 14th       N/A     0.292   0.380     0.380     N/A    N/A     N/A   -2.20
11:30, March 14th       N/A     0.291   0.360     0.380     N/A    N/A     N/A   -1.80
11:25, March 14th       N/A     0.292   0.360     0.380     N/A    N/A     N/A   -1.80
11:15, March 14th       N/A     0.316   0.380     0.390     N/A    N/A     N/A   -1.60
11:01, March 14th       ----------------- explosion in reactor building---------------
09:05, March 14th       N/A     N/A     0.450     N/A       N/A    N/A     N/A    N/A
09:00, March 14th       N/A     0.409   0.490     0.475     N/A    N/A     N/A   -1.50
08:00, March 14th       N/A     0.421   0.500     0.490     N/A    N/A     N/A   -1.00
06:50, March 14th       N/A     N/A     0.650     N/A       N/A    N/A     N/A    N/A
07:00, March 14th       N/A     0.439   0.520     0.500     N/A    N/A     N/A   -3.00
06:00, March 14th       N/A     0.282   0.425     0.400     N/A    N/A     N/A   dscale
05:00, March 14th       N/A     0.282   0.365     0.345     N/A    N/A     N/A   dscale
04:00, March 14th       N/A     0.260   0.340     0.325     N/A    N/A     N/A   -2.80
03:00, March 14th       N/A     0.235   0.315     0.305     N/A    N/A     N/A   -2.30
02:00, March 14th       N/A     0.178   0.275     0.275     N/A    N/A     N/A   -2.25
00:30, March 14th       N/A     0.152   0.255     0.255     N/A    N/A     N/A   -2.2

Containment pressure did fall after the explosion, but it rose again to higher levels. Not the behaviour I'd expect from a leaking containment. But there's also the possibility that the sensor, as so many others, already went to hell at that point.

Taken from:

http://gyldengrisgaard.dk/fukmon/uni3_monitor.html
 
  • #12,848
SteveElbows said:
Has anyone been able to identify any of the debris we see in the 5th video?

We seem to see main horizontal beams of the FHM that ran east-west across the pool. If we refer to the same video.
 
  • #12,849
clancy688 said:
Containment pressure did fall after the explosion, but it rose again to higher levels. Not the behaviour I'd expect from a leaking containment.

But that the containment was leaking after the explosion is obvious, for example "www.youtube.com/watch?v=iV_r5Ifp8-I&hd=1#t=44s" . What one has to consider is that probably after the blast, melting fuel kept off gassing and more corium kept forming, boiling water ever-more vigorously and thereby increasing the pressure.

The containment was not blown wide open, just enough small leak paths were blasted open to have allowed a mushroom-cloud of steam to escape in an instant of sudden explosive force. After the explosion, the force propelling depressurization falls and pressures build back up as corium keeps off gassing and boiling water.
 
Last edited by a moderator:
  • #12,850
clancy688 said:
That isn't consistent with pressure data (March 14th):

Indeed. Very thanks for the data. Then the explosion-like sudden decompression can be excluded.

However I think it's safe to assume that something had a leak there after/around the time of the explosion: the data shows steady downward trend without venting attempts.

Then maybe some more hydrogen stocked in the lower parts of the building can be an explanation?

SpunkyMonkey said:
... small leak paths...

I think small leak paths would not be enough for that big mushroom cloud. An overheated RPV would, but small leaks wouldn't.
 
  • #12,851
SpunkyMonkey said:
But that the containment was leaking after the explosion is obvious, for example "www.youtube.com/watch?v=iV_r5Ifp8-I&hd=1#t=44s" . What one has to consider is that probably after the blast, melting fuel kept off gassing and more corium kept forming, boiling water ever-more vigorously and thereby increasing the pressure.

The containment was not blown wide open, just enough small leak paths were blasted open to have allowed a mushroom-cloud of steam to escape in an instant of sudden explosive force. After the explosion, the force propelling depressurization falls and pressures build back up as corium keeps off gassing and boiling water.

Yeah, Id go along with that, although I am somewhat suspicious of the quality of various measurements too.
 
Last edited by a moderator:
  • #12,852
They did vent reactor 3 again several times (or at least once) after the explosive event didn't they?
 
  • #12,853
SteveElbows said:
Cheers.

On first viewing, videos 3 & 5 offer us some views that were not apparent from the previously released photos.

Has anyone been able to identify any of the debris we see in the 5th video?

Yes, we are again seeing parts from the NW corner of the FHM bridge, corresponding to the part closest to Quince in this photo of FHM2.
http://photo.tepco.co.jp/library/120228/120228_02.jpg

The FHM3 is quite similarly built, but as westfield notes it is not identical. A relevant difference here is that the FHM3 bridge has extra diagonal reinforcement beams built into the bottom section of the northern face of the bridge, as shown in this video (at about 2:25)
http://video.sina.com.cn/v/b/48514912-1822430771.html

The identifiable parts which we have seen of the FHM appear to be no longer attached to each other, nor to other parts to which they were attached. Separation appear to have occurred by breakage of interlinking bolts. I fear we will find this FHM to be thoroughly broken up and fubar.
 
  • #12,854
But there's also the possibility that the sensor, as so many others, already went to hell at that point.

one wonders what were they using for pressure indication? Got to put ourself in their shoes at the time:

we speculated at the time that with no electric power it was likely a mechanical pressure gage on the fire truck pumping into reactor that they used, hence readings would reflect the pressure drop along piping connecting the two. They'd be high when there is flow and accurate only at no flow. Operators would know to reduce flow to get a true reading, but the poor guy who's copying numbers for the record might not be so savvy. "Just read this gage and write it here every fifteen minutes"

I seem to remember looking at JStolfi's remarkable graphs and seeing correlation between flow and pressure. But that was a year ago.. don't trust my memory, 'cause i dont.
 
  • #12,855
clancy688 said:
<..>
Containment pressure did fall after the explosion, but it rose again to higher levels. Not the behaviour I'd expect from a leaking containment. But there's also the possibility that the sensor, as so many others, already went to hell at that point.
Taken from:
http://gyldengrisgaard.dk/fukmon/uni3_monitor.html
Those are earliest published data, and not the best available. Since then Tepco has assembled better and more complete data sets,
which yields better insight also in the period around the unit 3 explosion:
http://www.tepco.co.jp/nu/fukushima-np/f1/images/syusei_level_pr_data_3u.pdf

The impression of a rather sudden pressure drop concurrent with the explosion remains, however.

Data indicate to me that leading up to the event there was no longer any clear barrier between the atmosphere of the RPV, and the atmosphere of the primary containment. The whole system was well past design limits, the core was in the process of melting down, and the primary containment was probably already leaking to some degree. The sudden pressure drop in connection with the explosion is consistent with an assumed abrupt increase in leak area, resulting in a blow out of hydrogen and steam. One would expect such a blow out to be decreasing over time, as accumulated energy is being released from the system. In the case of unit 3, a rather vigorous evolution of steam was seen right after the explosion at 11 am, however this steam evolution swiftly subsided to become invisible before noon. (Only later in the afternoon unit 3 resumed steaming, apparently coincident with a renewed build up of pressure within the containment)
 
  • #12,856
One would expect such a blow out to be decreasing over time, as accumulated energy is being released from the system. In the case of unit 3, a rather vigorous evolution of steam was seen right after the explosion at 11 am, however this steam evolution swiftly subsided to become invisible before noon. (Only later in the afternoon unit 3 resumed steaming, apparently coincident with a renewed build up of pressure within the containment)

indeed if water that's pumped in as liquid comes out as steam through a constant leak area, one would expect strong flow^2 relation to pressure.
 
  • #12,857
It's heartening to see discussion of this topic, but also frustrating to know that the dedicated thread is lost. I wonder if the FHM really is in pieces. It wouldn't be much of a surprise if it were so, as it takes a lot of force to crumble concrete into small pieces like that.

It seems as if the #3 RPV was leaking hydrogen and steam at a fairly rapid rate even before the explosion. I was very skeptical regarding the theory of hydrogen going from Unit 3 into the others, but I am almost convinced, now.
 
  • #12,858
jim hardy said:
we speculated at the time that with no electric power it was likely a mechanical pressure gage on the fire truck pumping into reactor that they used, hence readings would reflect the pressure drop along piping connecting the two. They'd be high when there is flow and accurate only at no flow. Operators would know to reduce flow to get a true reading, but the poor guy who's copying numbers for the record might not be so savvy. "Just read this gage and write it here every fifteen minutes"

I find it unlikely that this was the source of pressure readings, since readings at various reactors were taken at moments when fire-trucks for reactor water pumping were not available, and we also have drywell and wetwell pressure readings.

Batteries were used to power existing instrumentation.
 
  • #12,861
http://www.tepco.co.jp/nu/fukushima-np/images/handouts_120416_04-j.pdf report on the recent nitrogen injection system failures (pressure swing adsorption)

http://www.tepco.co.jp/nu/fukushima-np/images/handouts_120416_03-j.pdf report on the recent contaminated water leak after reverse osmosis

http://www.tepco.co.jp/nu/fukushima-np/images/handouts_120416_02-j.pdf report on unit 4 SFP cooling system leak

http://www.tepco.co.jp/nu/fukushima-np/images/handouts_120416_05-j.pdf The plan to remove the remaining part of unit 4 reactor building roof
 
Last edited:
  • #12,862
These posts made me think of a scenario.
SpunkyMonkey said:
If it did so before the FHM fell, was it thrust at an almost horizontal angle like a javelin?
Rive said:
Then the explosion-like sudden decompression can be excluded...
...I think small leak paths would not be enough for that big mushroom cloud. An overheated RPV would, but small leaks wouldn't.
SteveElbows said:
I find it unlikely that this was the source of pressure readings, since readings at various reactors were taken at moments when fire-trucks for reactor water pumping were not available, and we also have drywell and wetwell pressure readings.
Readings were manually taken in intervals, yes?
Then it would be unlikely that explosion pressure/vacuum spike was recorded, right?
Could we then actually really exclude existence of such a spike?

And now my questions:
Could there have been a pressure surge ("explosion") in RPV/drywell which lifted concrete reactor seal a bit for a moment, propagating hydrogen explosion from drywell to maintenance floor 5, so pressing reactor concrete seals back into place, mostly undamaged except two or three points ("white steam leaks")?
If so, wouldn't pressure wave have been directed in a way that would lift up FHM from below sideways, and then push it horizontally like a javelin into the pool?
 
  • #12,863
Tepconium-311 said:
These posts made me think of a scenario.
Readings were manually taken in intervals, yes?
Then it would be unlikely that explosion pressure/vacuum spike was recorded, right?
Could we then actually really exclude existence of such a spike?

And now my questions:
Could there have been a pressure surge ("explosion") in RPV/drywell which lifted concrete reactor seal a bit for a moment, propagating hydrogen explosion from drywell to maintenance floor 5, so pressing reactor concrete seals back into place, mostly undamaged except two or three points ("white steam leaks")?
If so, wouldn't pressure wave have been directed in a way that would lift up FHM from below sideways, and then push it horizontally like a javelin into the pool?

The AEC transmitted a scenario where the head bolts stretched, which GE didn’t think was what happened.

"All the three units (IF] -3) experienced containment overpressure in the early phase of the accident, which caused excessive leakage from flange, ailocks and other peentrations. Hydrogen produced by Metal Water reaction in the core damage process must have escaped to the reactor building via this containment leakage path and accumulated on the top and caused deflagration/detonation there. Further, containment was steam inerted and a large fraction of hydrogen escaped -by “hardened” venting."

http://www.scribd.com/doc/89386167/AEC-Hydrogen-Analysis-Pages-From-C142015-02B
 
  • #12,864
Rive said:
I think small leak paths would not be enough for that big mushroom cloud. An overheated RPV would, but small leaks wouldn't.

How does an overheated RPV allow the big mushroom cloud to escape? Assuming just leaks, a steam explosion in the containment would force out a larger amount of steam than the slower steady lease from just boiling water. Imagine a plastic bottle you can squeeze and there's a steam generator in it with a steady amount of steam ejecting from leaks in the bottle. Then you suddenly squeeze the bottle with great force (simulating the explosion) and poof, a much bigger dose of steam shoots out the same leaks. No?

That aside, in "www.youtube.com/watch?v=VZoBb-8oxdg&hd=1" , the well cap is assumed to've been momentarily lifted, which is denoted as it falls back in place.
 
Last edited by a moderator:
  • #12,865
SpunkyMonkey said:
How does an overheated RPV allow the big mushroom cloud to escape?.

I mean: if all (or: most) of the overheated and pressurized water in the RPV is suddenly released (through a BIG hole) then it would be more than sufficient explanation for the secondary, mushroom-like cloud.

Just (relative) small leaks could not be able to carry out the necessary energy I think.

To turn it around: if that cloud were from the RPV then the release path would not be able to close itself and keep a relative high (or even just any over-) pressure after the explosion.

One more turn: I think we should assume that the energy of the secondary mushroom was also based on chemical reaction, and not on (or at least not mainly on) steam explosion.

(Sorry for my English.)

Ps.: Another possible explanation is that after the primary hydrogen explosion the escaping steam/hydrogen mixture burned for some seconds. That would require just a relative small hole, but it also would mean sufficient energy for a mushroom.
 
Last edited:
  • #12,866
Rive said:
I mean: if all (or: most) of the overheated and pressurized water in the RPV is suddenly released (through a BIG hole) then it would be more than sufficient explanation for the secondary, mushroom-like cloud.

I can see the need for a hole of a certain size, but not why it would have to be a hole in the RPV. A hole in the primary containment would seem quite fine for the job seeing the containment contained the main portion of the overheated water in the system. Indeed pressure readings indicate that the pressure in the PCV was higher than in the RPV leading up to the event. That could indicate that there was already a big hole connecting the RPV and the PCV, meaning any sudden leak to the upside would tap from both sources.

Just (relative) small leaks could not be able to carry out the necessary energy I think.

To turn it around: if that cloud were from the RPV then the release path would not be able to close itself and keep a relative high (or even just any over-) pressure after the explosion.

Perhaps we could have some reason to not trust the accuracy of the readings after the explosion? One failure mode could be the drying out of reference legs, which would if I understand result in faulty (too high) readings.

One more turn: I think we should assume that the energy of the secondary mushroom was also based on chemical reaction, and not on (or at least not mainly on) steam explosion.

(Sorry for my English.)

Ps.: Another possible explanation is that after the primary hydrogen explosion the escaping steam/hydrogen mixture burned for some seconds. That would require just a relative small hole, but it also would mean sufficient energy for a mushroom.

Considering the state the reactor was in, it stands to reason that any steam release from the containment could have included hydrogen possibly available for combustion, thus (only) adding heat to the mixture in the cloud. However, there would seem to me to be quite sufficient energy contained in the overheated water in the RPV/PCV, so I think perhaps it is an unnecessary assumption to make that combustion of hydrogen in the rising cloud played a significant role for its evolution.
 
  • #12,867
They have a different kind of robot which they are going to use to survey more of the torus of reactor 2 on the 18th:

http://www.tepco.co.jp/en/nu/fukushima-np/images/handouts_120417_03-e.pdf

I note that the building layout diagrams showing where it will go have a bit more detail than the ones they normally use. The resolution is barely good enough to read the labels but quite a number of them can be worked out if you zoom in on the pdf.
 
  • #12,868
  • #12,869
SteveElbows said:
They have a different kind of robot which they are going to use to survey more of the torus of reactor 2 on the 18th:

http://www.tepco.co.jp/en/nu/fukushima-np/images/handouts_120417_03-e.pdf

I note that the building layout diagrams showing where it will go have a bit more detail than the ones they normally use. The resolution is barely good enough to read the labels but quite a number of them can be worked out if you zoom in on the pdf.

I appreciate the fact that the sump pits are shown on the right hand diagram. It enables to narrow the possible locations for the pedestal opening ("slit").
 
  • #12,870
Indeed, pretty cool and detailed drawings this time, would like to walk through the plant to see how it looks in reality! Years ago I did such kind of drawings for other types of big industrial plants, but I have never been to an NPP.
 

Similar threads

  • · Replies 12 ·
Replies
12
Views
49K
  • · Replies 41 ·
2
Replies
41
Views
5K
  • · Replies 2K ·
60
Replies
2K
Views
451K
  • · Replies 5 ·
Replies
5
Views
6K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 6 ·
Replies
6
Views
20K
  • · Replies 763 ·
26
Replies
763
Views
274K
  • · Replies 38 ·
2
Replies
38
Views
16K
Replies
6
Views
4K
  • · Replies 4 ·
Replies
4
Views
11K