Japan Earthquake: Nuclear Plants at Fukushima Daiichi

Click For Summary

Discussion Overview

The discussion revolves around the technical aspects and current status of the nuclear plants at Fukushima Daiichi following the earthquake and tsunami in Japan. Participants are seeking reliable information regarding the operational conditions, safety measures, and potential risks associated with the nuclear reactors in the aftermath of the disaster.

Discussion Character

  • Exploratory
  • Technical explanation
  • Debate/contested

Main Points Raised

  • Some participants express skepticism about the reliability of media reports and emphasize the need for technical information from official sources like TEPCO and METI.
  • There are concerns regarding the reactor pressure levels, with reports suggesting that pressure may have exceeded safe limits, which some participants describe as a significant issue.
  • Questions are raised about the likelihood of a meltdown, with differing opinions on whether this is a realistic concern or media exaggeration.
  • One participant explains the role of coolant in a nuclear power plant, noting that it is essential for cooling the reactor and managing decay heat after shutdown.
  • There is discussion about the reactor's ability to be scrammed (shut down) and the implications of losing coolant, with some participants clarifying that decay heat continues to be produced even after shutdown.
  • Concerns are raised about the explosion of the containment building and its implications for safety, with speculation about the potential release of radioactive materials.
  • Participants discuss the wind direction at the time of the explosion and its potential impact on the dispersion of any radioactive materials released.

Areas of Agreement / Disagreement

Participants do not reach a consensus on the likelihood of a meltdown or the implications of the current situation at Fukushima Daiichi. There are multiple competing views regarding the severity of the situation and the reliability of information being reported.

Contextual Notes

Participants note the limitations of available information, including the reliance on second-hand reports and the challenges in verifying the status of the reactors and containment structures. There are also unresolved questions regarding the operational status of safety systems and the exact nature of the explosion.

  • #1,351
M. Bachmeier said:
So I guess containment, even in the case of a powerful explosion is factored into the design. The design seems to be such that energy from an explosion would be partially channeled either sideways or down or both. In the absence of more information I think I'll avoid speculation.

There is the problem of radioactive contamination from Unit 3. Specifically, this evidence I again summarize and put forward to review. It has been previously released by various sources and discussed in several of the preceding posts in this thread:

1) the timeline of radiation spikes shows the highest spike immediately following the blast at Unit 3.

2) it was reported that workers were initially pulled back after the explosion at Unit 3 because of concern of radiation after the blast.

3) it was reported access to Unit 3 was temporarily limited by high level radiation on the ground

4) it was reported that military tanks with dozer blades were to be brought into clear the radioactive debris so work could continue (no pictures of that I have seen, or confirmation that it actually happened as far as I know).

5) an unsourced diagram that showed the locations of the highest levels of measured radiation on the ground around Fukushima 1,2,3 and 4 shows the highest levels around Bldg 3 and has a positive correlation with visible debris blasted from the east, west, and south sides of Bldg 3, including some higher readings on the east side of Turbine Bldg 3 where side wall panels of Reactor Bldg 3 blew across the roof.

A counter hypothesis might be that the explosion at Bldg 4 was from the SFP and SFP4 hydrogen production, and that this may have been the source of high level radioactive debris (less likely, IMO). Even so, if that were possible, then it is equally possible that the same mechanism may have been at play in whole or in part in the explosion of Bldg 3.

Therefore, I conclude that the blast from Unit 3 carried high level radioactive waste with it.

If so, then regarding this high level waste in the explosion debris of Unit 3:
1) was it from the spent fuel pool of 3?
2) was it from the (damaged) reactor core of Unit 3?

Ultimately, those would seem to be the only two sources of high level ground debris.

3) how could an explosion, if powered only by vented hydrogen from the containment of Unit 3, and originating from the top floor of Bldg 3, disperse high level waste as ground debris from either of these sources?

Think about it.
 
Last edited:
Engineering news on Phys.org
  • #1,352
TCups said:
There is the problem of radioactive contamination from Unit 3. Specifically, this evidence I again summarize and put forward to review. It has been previously released by various sources and discussed in several of the preceding posts in this thread:

1) the timeline of radiation spikes shows the highest spike immediately following the blast at Unit 3.

2) it was reported that workers were initially pulled back after the explosion at Unit 3 because of concern of radiation after the blast.

3) it was reported access to Unit 3 was temporarily limited by high level radiation on the ground

4) it was reported that military tanks with dozer blades were brought into clear the radioactive debris so work could continue (no pictures of that I have seen).

5) a diagram that showed the locations of the highest levels of measured radiation on the ground around Fukushima 1,2,3 and 4 shows the highest levels around Bldg 3 and has a positive correlation with visible debris blasted from the east, west, and south sides of Bldg 3, including some higher readings on the east side of Turbine Bldg 3 where side wall panels of Reactor Bldg 3 blew across the roof.

A counter hypothesis might be that the explosion at Bldg 4 was from the SFP and SFP4 hydrogen production, and that this may have been the source of high level radioactive debris (less likely, IMO). Even so, if that were possible, then it is equally possible that the same mechanism may have been at play in whole or in part in the explosion of Bldg 3.

Therefore, I conclude that the blast from Unit 3 carried high level radioactive waste with it.

If so, then regarding this high level waste in the explosion debris of Unit 3:
1) was it from the spent fuel pool of 3?
2) was it from the (damaged) reactor core of Unit 3?

Ultimately, those would seem to be the only two sources of high level ground debris.

3) how could an explosion, if powered only by vented hydrogen from the containment of Unit 3, and originating from the top floor of Bldg 3, disperse high level waste as ground debris from either of these sources?

Think about it.

Well I've been considering some of the orange debris and wondered if some of it might not be a portion of the dry-well cap. And in keeping with your theory, a heavy steel dome shaped cap would be like the plate used in an explosive device for directional control (directional charge). In a dome like structure the point where it is attached to the upper reactor would seem a likely weak point, not to mention concerns that have been mentioned in the past about ensuring proper dry-well mounting.

If the orange debris is 3/4 inch steel section from the cap it would match your description sideways then upper energy release at unit 3.
 
  • #1,353
I've started to create this using all released data.. but it's kind of taking me to much time since I'm not using the appropriate tool (picture editor)
[PLAIN]http://k.min.us/imgwBU.gif
 
Last edited by a moderator:
  • #1,354
M. Bachmeier said:
Well I've been considering some of the orange debris and wondered if some of it might not be a portion of the dry-well cap. And in keeping with your theory, a heavy steel dome shaped cap would be like the plate used in an explosive device for directional control (directional charge). In a dome like structure the point where it is attached to the upper reactor would seem a likely weak point, not to mention concerns that have been mentioned in the past about ensuring proper dry-well mounting.

If the orange debris is 3/4 inch steel section from the cap it would match your description sideways then upper energy release at unit 3.

Somewhere, way back there, there was a post about the color scheme of painting various equipment in a nuc power plant. In short, there may be lots of stuff painted different colors, including red.

I doubt that the drywell cap has been completely blown off and even if so, that it were blown, it was not exploded, shrapnel-like, into many small pieces. More likely, it would be yet another bullet-like projectile, along with the drywell plug. But that is just my SWAG (scientific wild - guess) vs. WAG (wild - guess). Remember that the cap would tend to vent hydrogen gas into the upper portions of the dry wall containment and region of the fuel transfer chute and gate under as little as 2 ATM of pressure, if previous post references are correct.
 
  • #1,356
Refering to https://www.physicsforums.com/showpost.php?p=3210895&postcount=1342" and below plan the building is about 125 meters long (google earth)
then the flooded area is about 1650 m2

http://english.kyodonews.jp/news/2011/03/81133.html said:
Pools of water that may have seeped from either the reactor cores or spent fuel pools were
also found in the turbine buildings of the No. 2 and No. 4 reactors, measuring up to 1 meter
and 80 centimeters deep, respectively, while those near the No. 1 and No. 3 reactors were
up to 40 cm and 1.5 meters deep.
1 40cm
2 100cm
3 150cm
4 80cm
confirms that the source of the water is from unit 3 and has leaked into the neighbouring
units through cable tunnels. The cable tunnels would be fire proofed between the buildings
restricting the flow hence the varied heights

at the time of measurement volume of water is about 6000m3
 

Attachments

  • flood.jpg
    flood.jpg
    28 KB · Views: 714
Last edited by a moderator:
  • #1,357
|Fred said:
I've started to create this using all released data.. but it's kind of taking me to much time since I'm not using the appropriate tool (picture editor)

What is the significance of the red line at 4 atm?
 
  • #1,358
March 25' Areva's analyses of the case, i don't know if it is usefull or useless

http://www.scribd.com/doc/51564602?secret_password=th7hw1mmpjwnfmd0mbj
 
Last edited by a moderator:
  • #1,359
timeasterday said:
What is the significance of the red line at 4 atm?

That is supposed to be about the maximum design pressure of the primary containment. In theory it should hold for a pressure somewhat above 4 atm.
 
Last edited:
  • #1,360
Yes Astronuc, and according to this gentleman it sustained up to 8 before leaking http://www.ustream.tv/recorded/13414000
Now, What I 'm not sure to have right is: is this value is for the core (primary) or the drywell
 
Last edited by a moderator:
  • #1,361
|Fred said:
Yes Astronuc, and according to this gentleman it sustained up to 8 before leaking http://www.ustream.tv/recorded/13414000
Now, What I 'm not sure to have right is if this value is for the core (primary) or the drywell

refer to the attached for specification
 

Attachments

Last edited by a moderator:
  • #1,362
Can anyone direct me to information that would help quantify the differences in meltdown scenarios between MOX and non MOX fuel reactors?

i.e. all things being equal what is the additional risk?

Can we reasonably quantify it as some percent (5%) worse due to higher PU levels?

TIA, DWB
 
  • #1,364
I have a mundane question. Is Plutonium more toxic or radioactive than Uranium? I thought it was, but a spokesman from the Nuclear Safety Agency specifically denied this. Other "experts" seem to contradict his statement.
 
  • #1,365
Ivan Seeking said:
I have a mundane question. Is Plutonium more toxic or radioactive than Uranium? I thought it was, but a spokesman from the Nuclear Safety Agency specifically denied this. Other "experts" seem to contradict his statement.

Pu isotopes have shorter half-lives than the two main U isotopes, U-235 and U-238. Radiologically, the same number of atoms of Pu would be more radioactive.

Uranium dioxide fuel contains up to 5% U-235. The FK BWR fuel should have a peak enrichment around 4% U-235.

MOX might contain about 5%, which would be a mix of Pu-239, 240, 241 and 242. Pu-240 and Pu-242 also undergo spontaneous fission.

See attached figure.
 

Attachments

  • z93n144zl1ct127154.png
    z93n144zl1ct127154.png
    11.3 KB · Views: 380
  • #1,366
Astronuc said:
Pu isotopes have shorter half-lives than the two main U isotopes, U-235 and U-238. Radiologically, the same number of atoms of Pu would be more radioactive.

So he was lying? It was a flat denial. Could there be any other explanation for his answer?
 
  • #1,367
Ivan Seeking said:
I have a mundane question. Is Plutonium more toxic or radioactive than Uranium? I thought it was, but a spokesman from the Nuclear Safety Agency specifically denied this. Other "experts" seem to contradict his statement.

Chemical Toxicity I believe would be a yes. You do not want to snort Plutonium Oxide dust.
 
  • #1,368
Ivan Seeking said:
So he was lying? It was a flat denial. Could there be any other explanation for his answer?
I don't know the context. If he was referring to fresh fuel, he would be wrong. He might be thinking of irradiated UO2 and MOX fuel, which develop a similar array of fission products. In fact, UO2 becomes MOX fuel as it is irradiated.

How Pu is radiologically more hazardous than U.

Chemically, both being heavy metals, they may be comparable in toxicity.
 
  • #1,369
Why is it that in case of a shut down they bypass the turbine and route the steam directly to the condenser ?
 
  • #1,370
AntonL said:
Here is a time line of the explosions and reported CV venting
Unit 1 - 12.03.2011 at 15:36 : CVv 15:00 on 12.03.11
Unit 3 - 14.03.2011 at 11:01 : CVv 09:20 on 13.03.11
Unit 4 - 15.03.2011 at 06:14
Unit 2 - 15.03.2011 at 06:20 : CVv 11:55 on 13.03.11

There is a correlation between Unit 1 CV venting and Hydrogen blast.

Below SFP data FU = fuel units followed by pool volume and heat load of the FU
Unit 1 - 292 FU 1200m3 60kW
Unit 2 - 587 FU 1425m3 400kW
Unit 3 - 514 FU 1425m3 200kW
Unit 4 - 1331 FU 1425m3 2000kW + 200 brand new FU (yes 2MW not a typo)

This sets a new light on my earlier proposal
Unit 1 exploded due to H2 leak of venting system - possibly Earth quake damage
[STRIKE]Unit 2 to 4 exploded due to hydrogen generation from equipment pools.[/STRIKE]

https://www.physicsforums.com/attachment.php?attachmentid=33572&stc=1&d=1301164813

From above slide, and knowledge gained I revise what I posted earlier

Unit 1 - Explosion after venting - H2 leak in venting system
Unit 2 - Explosion at Torus - Torus has small leak, possibly a crack allowing H2 to vent.
Unit 3 - Explosion due to H2 leak at PVC-dome due to high pressure
Unit 4 - Explosion due to H2 generated in SFP
Core damage in all three working reactors.
And the water leak problem still to be found

Four units and four different failure modes leads to one conclusion:
BWR are not as safe as they are said to be. It is time to switch them off.


Conclusions already made by industry experts (see attached pdf file)
1. All existing power plants' passive emergency cooling systems (BWR's
RCIC and PWR's turbine-driven auxiliary feedwater system) should be inspected
and reinforced to assure their reliability during adverse condition. Onsite
emergency generators should be further protected.
2. PWR is more resilient than BWR because of its steam generator secondary
water inventory and size of containment. This gives larger margin to core damage
and containment failure. Further review is still necessary to improve the safety
level.
3. Spent fuel pool safety has been grossly overlooked. A hardened and
independent top spray system is necessary for all nuclear power plants.

Please read attached pdf file - the most authoritative analysis yet found.
 

Attachments

  • PCTRAN.pdf
    PCTRAN.pdf
    583 KB · Views: 277
  • explode.jpg
    explode.jpg
    46.6 KB · Views: 910
Last edited by a moderator:
  • #1,371
Regarding the multimile US hose reel systems in Okinawa I mentioned earlier that are now under consideration, and contaminated water handling now underway by tepco, I was considering the feasibility of pumping back into local lakes that are drained for freshwater via hose reel systems. They would of course first be lined by geomembrane to prevent groundwater intrusion. Ideally the lakes could concentrate the contamination via evaporation to then at sufficient concentration be drained, perhaps into collapsible membrane tanks.

The question I have is based on what we know about the radioisotope species in that basement water, would they be effectively concentrated via evaporation ponds?
 
  • #1,372
Ivan Seeking said:
I have a mundane question. Is Plutonium more toxic or radioactive than Uranium? I thought it was, but a spokesman from the Nuclear Safety Agency specifically denied this. Other "experts" seem to contradict his statement.

I found something here:
http://www.tpub.com/content/doe2/doe-std-1128-98_ch1/doe-std-1128-98_ch10039.htm

"...The radiological toxicity of reactor-produced plutonium far exceeds the
chemical toxicity of this heavy element..."
..."In contrast to uranium, the chemical
toxicity of plutonium is insignificant in comparison to the hazard arising
from its natural radioactivity." Moreover, "the toxicity of plutonium and
other transuranic elements," according to Voelz et al. (1985), "has only
been studied in animals since acute toxicity has never been observed in
man for these elements and epidemiologic studies have not produced
positive results." ...
 
  • #1,373
|Fred said:
Yes Astronuc, and according to this gentleman it sustained up to 8 before leaking http://www.ustream.tv/recorded/13414000
Now, What I 'm not sure to have right is: is this value is for the core (primary) or the drywell

Note the significant bolting of the Drywell Cap and the fact it has a relief valve on it. There is the hydrogen release point, if indeed the pressure rose to 8 atm. Normally reliefs are set at 125-150 percent of design relief pressure. That is unless the 4 atm included a 150 percent safety factor.
 
Last edited by a moderator:
  • #1,374
AntonL said:
https://www.physicsforums.com/attachment.php?attachmentid=33572&stc=1&d=1301164813

From above slide, and knowledge gained I revise what I posted earlier

Unit 1 - Explosion after venting - H2 leak in venting system
Unit 2 - Explosion at Torus - Torus has small leak, possibly a crack allowing H2 to vent.
Unit 3 - Explosion due to H2 leak at PVC-dome due to high pressure
Unit 4 - Explosion due to H2 generated in SFP
Core damage in all three working reactors.
And the water leak problem still to be found

Four units and four different failure modes leads to one conclusion:
BWR are not as safe as they are said to be. It is time to switch them off.


Conclusions already made by industry experts (see attached pdf file)
1. All existing power plants' passive emergency cooling systems (BWR's
RCIC and PWR's turbine-driven auxiliary feedwater system) should be inspected
and reinforced to assure their reliability during adverse condition. Onsite
emergency generators should be further protected.
2. PWR is more resilient than BWR because of its steam generator secondary
water inventory and size of containment. This gives larger margin to core damage
and containment failure. Further review is still necessary to improve the safety
level.
3. Spent fuel pool safety has been grossly overlooked. A hardened and
independent top spray system is necessary for all nuclear power plants.

Please read attached pdf file - the most authoritative analysis yet found.

Anton: At glance, I'd say you missed something on the Japanese slide. Look again, Grasshopper!

Unit 1 - Explosion after venting - H2 leak in venting system
Unit 2 - Explosion at Torus - Torus has small leak, possibly a crack allowing H2 to vent.
Unit 3 - Explosion due to H2 leak at PVC-dome due to high pressure AND H2 from SFP
Unit 4 - Explosion due to H2 generated in SFP


But more to read. Thanks.
 
Last edited by a moderator:
  • #1,375
http://news.yahoo.com/s/ap/as_japan_earthquake;_ylt=Ao6GXsSDQnvGdeAge5aI74Os0NUE;_ylu=X3oDMTNrMTVydHNzBGFzc2V0A2FwLzIwMTEwMzI2L2FzX2phcGFuX2VhcnRocXVha2UEY2NvZGUDbW9zdHBvcHVsYXIEY3BvcwMzBHBvcwMxMARwdANob21lX2Nva2UEc2VjA3luX3RvcF9zdG9yeQRzbGsDamFwYW5zZ292ZXJu" :
Defense Minister Yoshimi Kitazawa said late Friday that the U.S. government had made "an extremely urgent" request to switch to fresh water. He said the U.S. military was sending water to nearby Onahama Bay and that water injections could begin in the next few days.

The U.S. 7th Fleet confirmed that barges loaded with 500,000 gallons of fresh water supplies were on their way.

At least someone seems to be worried about the Cl-38.
 
Last edited by a moderator:
  • #1,376
I have a mundane question. Is Plutonium more toxic or radioactive than Uranium? I thought it was, but a spokesman from the Nuclear Safety Agency specifically denied this. Other "experts" seem to contradict his statement.
Plutonium is far more hazardous than Uranium. Plutonium has a very high specific activity as compared to Uranium. It takes very little Plutonium to cause radiological damage from the alpha particles once inhaled. As I recall a lung burden of Plutonium is around 16 nanoCuries.
In the case of MOX fuel once the plutonium is encased in the fuel assembly and undergoes fission the resulting fission yield curves are close to the Uranium fission yields and the fission products become a higher hazard level than Plutonium. Again look at the specific activities.
 
  • #1,377
Fukushima Nuclear Accident Update (26 March 2011, 15:15 UTC)

The IAEA has been informed by Japanese authorities that fresh water is now being used in place of sea water to cool the reactor pressure vessels at Units 1, 2 and 3 at the Fukushima nuclear power plant. The switch to fresh water is preferable as it leaves fewer deposits in components and is less corrosive than sea water.

http://www.iaea.org/newscenter/news/tsunamiupdate01.html

Will they now vent less steam in order to wash away as much salt as possible?



oh, a couple of people asked two pages back whether or not it was speculation that the pressure gauges in 2 and 3 were malfunctioning. This from IAEA yesterday:

Reactor pressure is decreasing at Unit 1 and so is seawater injection. On the other hand, pressure readings in the reactor pressure vessels remain unreliable in Unit 2 and have become unreliable in Unit 3

But see this from latest JAIF report:

Reactor 2:

Reactor pressure (26th 10:40)
(A) -0.014MPaG, (B) -0.016MPaG

CV pressure (26th 10:40)
0.115MPaabs

Reactor 3:

Reactor pressure (26th 10:00)
(A) 0.038MPaG, (B) -0.101MPaG

CV pressure (26th 10:00)
0.1066MPaabs​

http://www.jaif.or.jp/english/news_images/pdf/ENGNEWS01_1301137974P.pdf

(reactor pressure readings are gauge, not absolute)

So it appears the pressure gauges in 2 and 3 may be functional and the pressures therein are equal to atmospheric.
 
Last edited by a moderator:
  • #1,378
|Fred said:
Why is it that in case of a shut down they bypass the turbine and route the steam directly to the condenser ?
The by-pass is done to protect the turbine. It is afterall a steam turbine, not a water turbine. The low pressure turbine has espeically long blades that could be damage if they where sloshing through water. The by-pass is usually done with a minimal flow of steam.
 
  • #1,379
Astronuc said:
The by-pass is done to protect the turbine. It is afterall a steam turbine, not a water turbine. The low pressure turbine has espeically long blades that could be damage if they where sloshing through water. The by-pass is usually done with a minimal flow of steam.

You might also want to add that if the Generator has been disconnected from the Electrical Grid the Turbine would be driving a light load, even through the numerous reductions gears. The amount of steam to drive a turbine with a very light load is very small, while you can dissipate a lot of heat energy if the condenser is designed for that purpose.

For those who are first time readers, after you have a Reactor scram, you still have to dissipate a lot of heat. If a Reactor scrammed in an Earthquake it is most likely that the Turbine shut off valve also tripped to protect the turbine (as much as possible as the Earth is jumping.)

The only place where you can send the reactor steam is to the condenser.
 
  • #1,380
Btw - who produces the MOX used in #3? I read that it came from France?
 

Similar threads

  • · Replies 12 ·
Replies
12
Views
50K
  • · Replies 41 ·
2
Replies
41
Views
6K
  • · Replies 2K ·
60
Replies
2K
Views
465K
  • · Replies 5 ·
Replies
5
Views
6K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 6 ·
Replies
6
Views
21K
  • · Replies 763 ·
26
Replies
763
Views
281K
  • · Replies 38 ·
2
Replies
38
Views
16K
Replies
6
Views
4K
  • · Replies 4 ·
Replies
4
Views
12K