Maximum Short Circuit Current (Fault-Current) before breakdown of cond
The discussion focuses on calculating the short circuit current for a three-phase cabinet operating at 400V/415V with an initial fault current of 46 kA for 1 second. Participants seek methods to determine the short circuit current for longer durations, specifically 3 seconds, and explore the relationship between current and time. The formula I² × t = constant is highlighted, indicating that the short circuit current decreases over time from its peak value. Additionally, the discussion emphasizes the importance of busbar design to withstand maximum instantaneous short circuit currents without exceeding thermal limits. The calculations provided illustrate how system impedance influences short circuit current values.
tipu_sultan
Here find some attached circuit of three phase cabinet which operation voltage is 400V /415V and have operated current 800A, fault current for 1 sec is 46 KA and have incoming and outgoing links with one phase Lighting and socket.
I want to know is there some method that one can calculate the short circuit current per second that the bus-bar can bear.
Moreover I also want to calculate the short circuit current for 3 second.
Is there any relation between the current and time in this case (directly, or Inversely Proportion) ?
Please provide me the formula if exist to calculate short circuit current (fault-current) in any time.
Product of I2 X t = constant
think about that... can you explain why?
The short-circuit current presents different values significant for withstand calculation:
ip[peak value] =k*sqrt(2)*I”k [IEC 60909-1 definition]
k=1.7-1.9[max.2] depending on X/R of the short-circuit grid.
it is the highest possible instantaneous value of the short-circuit current.
I”k = Initial symmetrical short-circuit current [rms].
The electromagnetic effect a circuit [physical] element has to withstand is defined as maximum force acting on this element. For three-phase short-circuit [according IEC 60865-1]:
Fm3=miuo/(4 *pi())*sqrt(3)*ip^2/am pi()=3.14159... [in excel language] am=distance between elements[busbars].
As you can see this value does not depends on time and in any case the busbar has to withstand it.
So you cannot allow a more elevated value of the short-circuit current.
The short-circuit current in time will decrease from I”k up to Ik-steady state short-circuit and in this time the losses produced in busbars have to be limited so not to heat the circuit element more than permitted.This is the thermal effect which the busbar has to withstand.
If Ithr =rated short-time withstand current
Tkr=rated short-time
If the new current Ith is LESS than Ithr then:Ith<=Ithr*sqrt(Tkr/Tk) Tk=new short-time.Tk>Tkr
If Tk<Tkr the new current has to be NOT MORE than Ikr in any case.
So 46 kA for 1 sec [rated] could be 26.55 kA for 3 sec.
The steady state load current [not for short-time] depends on the downstream consumers [motors, other panels and so on].Short-circuit current depends on upstream [the supply system-utility or generators, the transformer, the low voltage cables] impedance.
For instance, let’s say the transformer ratings will be 2500 kVA/ 415V. If the short-circuit voltage will be 6% then the transformer impedance will be: 6/100*0.415^2/2.5=0.004133 ohm. Neglecting the resistance then Xtrf=Ztrf
The supply system for medium voltage short-circuit apparent power Ssys=500 MVA and system impedance will be:
Zsys [at 415 V system]=0.415^2/500=0.0003445 ohm and neglecting the resistance Xsys=Zsys.
A low voltage cable [2 parallel cables of 3*240 mm^2 copper conductors 90oC insulation- for 2*400A rated current] presents a resistance approx.0.0947 ohm/km and a reactance of 0.0819 ohm/km. The length of cable [let’s say] =17 m and the cable impedance will be:
Zcab=0.000805+j.0.000696 ohm. Total impedance will be:
Xtot=0.0003445+0.004133+0.000696=0.00517 ohm
Ztot=sqrt(0.00517^2+0.000805^2)=0.00523 ohm I”k3= three phases short-circuit current [metallic contact-no arcing].
I”K3=VoltL_L/sqrt(3)/Ztot=0.415/sqrt(3)/0.00523=45.8 kA.
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
Thread 'Beauty of old electrical and measuring things, etc.'
Even as a kid, I saw beauty in old devices. That made me want to understand how they worked. I had lots of old things that I keep and now reviving. Old things need to work to see the beauty. Here's what I've done so far. Two views of the gadgets shelves and my small work space: Here's a close up look at the meters, gauges and other measuring things: This is what I think of as surface-mount electrical components and wiring. The components are very old and shows how...