"I wanted to ask, the factors you mentioned in the examples in your last post such as: [PWR]
- Colder inlet temps = increases in reactor power (Why is this?)
- T_ave/T_ref control
- "Average reactor temperature drops slightly, as a result of this power increase"
- "Now I need to raise average temperature to maintain it equal to reference temperature"
Do these occur in a BWR or are they strictly characteristics of a PWR? or are they automatically dealt with due to the automatic pressure control of the turbine?"
These are PWR characteristics. In a BWR at power, the unit is always held at saturation. This means BWR temperature is locked in by pressure in the reactor. Heatup and cooldown are controlled by changing reactor pressure, which isn't normally done during operation. For my BWR, we do not exceed ~10% power until we are at rated pressure. Once we get there, we don't look at temperature again until we come offline, and only monitor pressure to make sure the turbine is responding correctly.
As for colder water making power go up. Colder water removes more heat, and is also more dense, this improves both neutron moderation as well as neutron absorption characteristics in the core, allowing more neutrons to get moderated and more neutrons to return to the fuel to cause fission.
What do you mean by "rod pattern" and "core re-circulation flow"
So to recap BWR operation, you would use the control rods until 50% after which the re-circulation flow would take over? and the re-circulation flow would be getting pressure feedback from the turbine so it can adjust itself to increase reactivity I assume thus lowering/increasing reactor pressure??
So control rods are used to raise power up till around 45-50%. At this point, we start raising up the cooling water flow rate in the reactor. Raising the flow rate causes the steam to leave the reactor more rapidly. The steam bubbles are bad moderators, they don't slow neutrons down. If you push the bubbles out faster, the bubbles spend less time in the core, meaning more liquid water is available for moderation. This causes power to go up.
Normally the turbine is in pressure control mode. In this mode, if pressure starts to go up, the turbine throttles open to draw more steam, and pressure stops going up. This makes more electricity. If pressure starts to go down, the turbine throttles close to draw less steam, and pressure stops going down. So for the reactor, this means if I raise power, the turbine will automatically raise output, and pressure remains nearly constant. Normally recirculation doesn't get any feedback and is in manual control.
In the BWRs with automatic flux control enabled (many/most BWRs in the US don't use this anymore), recirculation will get feedback from the pressure regulator and from the flux monitors to try and hold pressure and power steady. In these plants you can run the turbine in "load set" mode, where you demand X megawatts, and the reactor tries to automatically follow. This is disabled in most plants because advanced core designs put the plant in a mode where you have very tight fuel thermal limits, and manual power control is preferred.
- Is the pressure that the turbine requires a set number or does it fluctuate?
How pressure control mode works for the turbine: You set the "zero power" pressure in the regulator. For example, my plant is 917 PSIG at zero percent power output. Then, as main steam pressure goes up from there, the turbine opens it's throttle valves for pressure control. For my plant, at 100% steam output, the turbine controls pressure 30 PSIG higher than the setpoint and all valves are about full open.
- Why is reactor pressure more important than delivering pressure to the turbine?
For a BWR, if you have the turbine simply draw more steam than is being produced, reactor pressure will drop. Lowering reactor pressure causes water to flash to steam, increasing the steam voids in the core, which further reduces power, and causes pressure to drop even more. The opposite is also true. As a result, unless you have an automatic flux control mode for your recirculation pumps, you can't operate the turbine in Load Set mode.
- What happens if the reactor is completely depressurized?
When you are completely depressurized, shut down cooling will subcool the reactor. This is the only time you really are controlling reactor temperature directly. You line up a heat exchanger directly on the reactor and just keep it cold and subcooled.
Between cold shutdown at about 15% power, reactor power is controlled by rods, and reactor pressure is controlled by using the steam dumps.
I just want to clarify a few other things, when you say global power control. I assume you mean the power output at the generators?
So what would core power be in relation to then?
What I mean with this, is that depending on where the control rod is in the core, it can sometimes change only the neutron flux profile directly around it, or across the entire core. When the rods are in the bottom 1/3rd of the core, they only change the "shape" of the neutron flux, and don't affect total core power much at all. When the rods are 2/3rds or more inserted, moving them will affect total core power.
A few other questions in regards to BWR's if constant pressure is maintained why would reactor power ever go down? what would be examples of disturbances to the system?
Power goes down if you lose recirculation flow, or insert control rods. So if I insert a control rod at power, core power decreases, and the turbine will sense this and throttle the turbine valves shut to hold pressure steady. The reactor now sits at steady state, at a lower power level.
Some disturbances, recirculation pump trip, control rod spurious insertion, loss of feedwater heaters (causes colder water to go into the core, this causes core power to go UP fast). Pressure regulator malfunctions can cause power changes, but typically these happen so fast that you'll scram before you can respond to them. Also, if you have one of your main feedwater pumps trip, the recirculation pumps will rapidly ramp down core cooling flow, voiding the core out and causing a rapid power drop. After the voiding is complete, power is low enough that the one remaining feedwater pump has enough capacity to keep the water level in its normal band.
I like answering these questions, hope this helps!