SUMMARY
The discussion focuses on designing a proportional controller for a twin water tank system to achieve a 10% steady state error. The closed loop transfer function (CLTF) is derived using the parameters Go = 4.0, α = 0.168, β = 0.0047, and Z1 = 8.9. The method for calculating the proportional gain (kp) involves evaluating the limit of the transfer function as s approaches zero, specifically T(0) = kpG0Gsens/(β + GsensCG0z1). The importance of isolating pole and zero locations is also highlighted, although it is noted that finding poles is unnecessary for steady-state error calculations.
PREREQUISITES
- Understanding of closed loop transfer functions (CLTF)
- Familiarity with proportional controller design
- Knowledge of the final-value theorem in control systems
- Basic concepts of pole and zero analysis in transfer functions
NEXT STEPS
- Study the derivation of closed loop transfer functions in control systems
- Learn how to compute proportional gain (kp) for various control systems
- Explore the final-value theorem and its applications in steady-state analysis
- Investigate pole and zero placement techniques in control system design
USEFUL FOR
Control system engineers, students studying feedback control, and anyone involved in designing proportional controllers for dynamic systems.