Paralleled Transformers: Why Overload & How to Prevent It?
  • Thread starter Thread starter Nahian
    Transformer
When transformers with identical turns ratios but varying kVA ratings are paralleled, the smaller transformer may become overloaded while the larger one remains underloaded due to differing impedances. This imbalance occurs because power and current distribution between the transformers does not align with their kVA ratings. To prevent overload, it is crucial to analyze the system using mathematical calculations or load-flow modeling software. Properly managing the impedance and ensuring balanced loading is essential for safe operation. Understanding these dynamics is vital for effective transformer management in parallel configurations.
Nahian
When transformers with the same turns ratio, but different kVA ratings are paralleled , it is possible for the smaller transformer to be overloaded and the larger transformer to be lightly loaded.Why is it so? Can anyone please show mathematical and theoretical explanation?And what can be done to stop the overloading of the transformer?
The impedances will be different. Therefore, the sharing of power and current between the parallel branches will not necessarily be in proportion to their KVA ratings.
If you can't do the calculations by hand, any load-flow program modeling those transformers in parallel will calculate the splits in current and power.
Thanks
Then you are creating a loop - through transformer A and back through transformer B. Be very careful!
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...