I sense a hint of sarcasm...
‘Don’t daisy-chain power strips’ is a rule that everyone seems to know, but no one knows quite why, hence the lively discussions. Surely if you have a 16A breaker protecting the circuit, and the power strips are appropriately rated, there should be no problem - if you overload the setup, the breaker will trip.
It’s not so much the length, but the smaller conductor size (0.75mm2 on the one next to me, versus 2.5mm2 for the fixed wiring), and the infrequently used connections, which often make poor contact.
A typical UK ring main, protected by a 32A B breaker, has a max loop impedance of 1.16 ohms (BS 7671). If the external loop is at the 0.8 ohm maximum for TN-S supplies, that doesn’t leave much to play with before exceeding the specs for disconnection times, adding in the fixed wiring and two or three power strips.
If it’s not that, then what is the problem with doing this?