Pressure reduction and increased volume

AI Thread Summary
The steam generator designed for natural gas requires a pressure of 2000-4000 mmAq and consumes 71 Nm3/h, but when switching to LPG, the existing pressure regulator is inadequate for maintaining sufficient gas volume. Propane has a higher energy content, meaning less volume is needed, but the user has already implemented a smaller orifice without success. The air/gas mixture remains suboptimal, leading to an improper flame and lockout issues. The manufacturer suggests using multiple LPG cylinders in parallel to increase volume, prompting the need for a suitable regulation method for this setup. Proper regulation and configuration are essential for successful operation with LPG.
asami58
Messages
2
Reaction score
0
Hi. Can someone help me please.
I have a steam generator which is designed to operate from natural gas with pressure of 2000 -4000 mmAq. It consumes a volume of 71 Nm3/h of the gas. I want to operate it on Liquid Petroleum Gas (LPG-Propane). The problem is that LPG is available in cylinders at a pressure of 150 to 200 psi. I used a pressure regulator to bring down the pressure to required limits, but the system locks out because it is not getting sufficient volume of the gas. How can I provide it with the required volume and pressure from an LPG cylinder?
 
Engineering news on Phys.org
Welcome to PF.

Your regulator must be set too low: propane has a higher energy content per unit volume than natural gas so you actually need less of it. So actually, in addition to the regulator, you may need a smaller orifice to allow less flow at the same pressure. See if your manufacturer has a conversion kit.
 
Hi Russ
Thanks for the reply. Firstly, the manufacturers (Booster Boiler Co Ltd, Korea) don't have a conversion kit. Secondly, i did use a smaller orifice (the LPG cylinder valve allows for about 0.25" nozzles). Originally, the unit requires a 2" dia inlet pipe for the gas, I used a 0.25" nozzle. It allows the pressure to be regulated, but somehow the volume isn't sufficient. The air/gas mixture not being optimum, the flame is not blue enough and the flame detector gives a lockout. The company has advised I use multiple cylinders in parallel, which brings me to the point of wanting to know how to regulate the combination?
 
Hi all, I have a question. So from the derivation of the Isentropic process relationship PV^gamma = constant, there is a step dW = PdV, which can only be said for quasi-equilibrium (or reversible) processes. As such I believe PV^gamma = constant (and the family of equations) should not be applicable to just adiabatic processes? Ie, it should be applicable only for adiabatic + reversible = isentropic processes? However, I've seen couple of online notes/books, and...
Thread 'How can I find the cleanout for my building drain?'
I am a long distance truck driver, but I recently completed a plumbing program with Stratford Career Institute. In the chapter of my textbook Repairing DWV Systems, the author says that if there is a clog in the building drain, one can clear out the clog by using a snake augur or maybe some other type of tool into the cleanout for the building drain. The author said that the cleanout for the building drain is usually near the stack. I live in a duplex townhouse. Just out of curiosity, I...
I have an engine that uses a dry sump oiling system. The oil collection pan has three AN fittings to use for scavenging. Two of the fittings are approximately on the same level, the third is about 1/2 to 3/4 inch higher than the other two. The system ran for years with no problem using a three stage pump (one pressure and two scavenge stages). The two scavenge stages were connected at times to any two of the three AN fittings on the tank. Recently I tried an upgrade to a four stage pump...
Back
Top