Pressure Transmitter Installation at 410 deg C

AI Thread Summary
The discussion revolves around the installation of a pressure transmitter that must operate at a maximum process temperature of 420 deg C, while the transmitter itself can only withstand up to 350 deg C. To mitigate this issue, the plan involves extending the tubing length to reduce the temperature at the transmitter connection to 310 deg C. Key considerations include the choice of tubing material, with 316/316L stainless steel being preferred due to its lower thermal conductivity compared to copper. The ambient temperature and wind speed are also factors that will influence the heat transfer, suggesting the need for a coiled or zig-zagged tubing design to enhance cooling. Ultimately, the goal is to ensure the transmitter operates safely within its temperature limits.
ednalds
Messages
2
Reaction score
0
Hi,

I have an application of pressure transmitter at 410 deg C max. process temperature. Transmitter can withstand only up to 350 C at Atm pressure.
The original length of tubing for maximum working Temp of 310 C is shown in the attach file (Sketch B) and We are planning to extend the length of tubing
so the temperature will decrease from 410 C (process side) to 350 C or even to 310 C (at transmitter connection). Maximum ambient air temperature is 65 deg C. Maximum pressure we are measuring is 0.6 inH2O.
Is there anyone can help me to have the formula to calcualte the length of tubing, X in the attached sketch A?

Thank you.

Regards,
Edmund
 

Attachments

  • 410 deg C Installation.JPG
    410 deg C Installation.JPG
    15.2 KB · Views: 508
Physics news on Phys.org
I don't have an equation to solve your problem, but I can suggest some points to consider. The first is that we don't know the diameter, thickness, or material of the tube. For example, copper conducts heat very well, but stainless steel is not a very good conductor. So this suggests your pickup tube needs to be made from stainless steel. The next issue is that it's not clear if the ambient air is moving or not. Still air is a very poor conductor of heat which suggests you'll need forced air or some sort of heat sink.

I'll suggest a tube made from the smallest diameter stainless steel tube that will work for you, and have it coiled or zig-zagged against a good heat sink.
 
Hi, Ryoko.

Thanks for the response.

Here the new info I got from our design standard.
Tube Material: 316/316L SS
Tube Diameter: 1" (But we will try to propose 1/2" if needed) Sch 80
OD / ID: 3.34 / 2.43 cm for 1" dia.
2.13 / 1.39 cm for 1/2" dia
Ambient Normal maximum temperature (hottest month) is 44 deg C with an average of 37 deg C. The previous 65 deg C temp is only our design temp.
Maximum basic Wind Speed, 3 sec. gust (at 10 m above ground for 50-year mean recurrence intervals) is 155 km/hr.
The device will be installed at 13 and 14 meters above ground.
New process Temp is 420 deg C instead of 410.
Required Temperature at the end of tubing is 310 deg C.

Coiled or zig-zagged can also help to minimize the space.

Regards,
Edmund
 
The rope is tied into the person (the load of 200 pounds) and the rope goes up from the person to a fixed pulley and back down to his hands. He hauls the rope to suspend himself in the air. What is the mechanical advantage of the system? The person will indeed only have to lift half of his body weight (roughly 100 pounds) because he now lessened the load by that same amount. This APPEARS to be a 2:1 because he can hold himself with half the force, but my question is: is that mechanical...
Hello everyone, Consider the problem in which a car is told to travel at 30 km/h for L kilometers and then at 60 km/h for another L kilometers. Next, you are asked to determine the average speed. My question is: although we know that the average speed in this case is the harmonic mean of the two speeds, is it also possible to state that the average speed over this 2L-kilometer stretch can be obtained as a weighted average of the two speeds? Best regards, DaTario
Some physics textbook writer told me that Newton's first law applies only on bodies that feel no interactions at all. He said that if a body is on rest or moves in constant velocity, there is no external force acting on it. But I have heard another form of the law that says the net force acting on a body must be zero. This means there is interactions involved after all. So which one is correct?