A leading power factor indicates that the current leads the voltage, resulting in a negative angle when calculating the power factor angle. The formula for power factor is defined as pf = cos(θ_V - θ_I), where a positive result signifies a lagging current. In the case of a leading power factor, the angle θ_V - θ_I becomes negative, confirming that the current is ahead of the voltage. Understanding this relationship eliminates the need for memorization of rules regarding negative signs. This clarification helps in accurately determining power factor angles in electrical systems.
FrogPad
Messages
801
Reaction score
0
I just took an exam, and one of the questions had a load with a power factor that was leading. ALL of our examples have dealt with LAGGING power factors, so I was unsure about determining the angle.

So for example)
Find the power factor angle of the following load (load 1):

pf_{load1}=0.9\,\,\,LEADING

would the angle be negative? like...
\theta_{z\,\,load1}=-\cos^{-1}(0.9)
 
Physics news on Phys.org
Hi there,

The answer to your question is "yes". The power factor is defined as: pf=\cos(\theta_V-\theta_I). The terms "leading" and "lagging" pertain to the relationship that the current has with respect to the voltage.

So when you have \theta_V-\theta_I>0, the current lags the voltage and the power factor is said to be "lagging". When the current leads the voltage then we have \theta_I>\theta_V, which of course implies that the argument of the cosine function, \theta_V-\theta_I, is negative.
 
Thank you for the thorough reply. I really didn't want to just memorize that I should toss a negative sign in there. Thanks for the background :smile:
 