Transformers are rated in KVA (kilovolt-amperes) rather than KW (kilowatts) because KVA measures apparent power, which accounts for both real power and reactive power. The relationship between real power and apparent power is defined by the power factor, which can be less than one due to the load's reactance. This means that the actual power consumed may differ from the apparent power, making KVA a more accurate representation of a transformer's capacity. Using KVA ensures that the rating reflects the total power handling capability of the transformer without being affected by the power factor. Therefore, transformers are rated in KVA to provide a clearer understanding of their performance under varying load conditions.
ikram_dp
Messages
3
Reaction score
0
why is the Rating of Transformer is in KVA and not in KW?
 
Last edited by a moderator:
Engineering news on Phys.org
VA (volt-ampere) is the unit for apparent power. W(watt) is the unit for real power. The relation between the two is:

real power = power factor \cdot apparent power

The load that you may connect to a transformer could have a reactance which results in a power factor less then 1 for the load and so the total power consumed by the load would be it's apparent power (expressed in VA) and not it's real power (expressed in W). That's why the power rating of a transformer is given in VA and not in W.

Check this Wikipedia articles on:
AC power
Power factor
 
Last edited:
thanx for help.
 
Very basic question. Consider a 3-terminal device with terminals say A,B,C. Kirchhoff Current Law (KCL) and Kirchhoff Voltage Law (KVL) establish two relationships between the 3 currents entering the terminals and the 3 terminal's voltage pairs respectively. So we have 2 equations in 6 unknowns. To proceed further we need two more (independent) equations in order to solve the circuit the 3-terminal device is connected to (basically one treats such a device as an unbalanced two-port...
suppose you have two capacitors with a 0.1 Farad value and 12 VDC rating. label these as A and B. label the terminals of each as 1 and 2. you also have a voltmeter with a 40 volt linear range for DC. you also have a 9 volt DC power supply fed by mains. you charge each capacitor to 9 volts with terminal 1 being - (negative) and terminal 2 being + (positive). you connect the voltmeter to terminal A2 and to terminal B1. does it read any voltage? can - of one capacitor discharge + of the...
Thread 'Weird near-field phenomenon I get in my EM simulation'
I recently made a basic simulation of wire antennas and I am not sure if the near field in my simulation is modeled correctly. One of the things that worry me is the fact that sometimes I see in my simulation "movements" in the near field that seems to be faster than the speed of wave propagation I defined (the speed of light in the simulation). Specifically I see "nodes" of low amplitude in the E field that are quickly "emitted" from the antenna and then slow down as they approach the far...
Back
Top