Resistive load bank testing for generator

AI Thread Summary
In the discussion on resistive load bank testing for generators, a technician questions the interpretation of power factor when load banking a 25kVA generator. The technician believes that since the load bank is purely resistive with a power factor of 1.0, they can apply the maximum current of 30.1 amps as indicated on the generator's data plate. However, the consensus is that the generator's active power capacity must be considered, which is limited by its power factor of 0.8, resulting in a maximum allowable current of 24 amps. Additionally, a user discusses the design of a resistive load bank rated for 30 kW, emphasizing that it accommodates the maximum current drawn while addressing concerns about its specifications. Understanding both electrical and mechanical limitations is crucial for accurate load bank testing.
pic498
Messages
1
Reaction score
0
Ok, so here's my scenario/question. I am a technician that works on generators and does load bank testing on them. I'm having a debate with my boss about power factor and IF I'm wrong--I would like to understand why.
Today I load banked a generator that was rated at 25kVA and could run at 120/240 single phase, 120/208 3 phase, or 277/480 3 phase. I was running the generator on the 480 setting and, according to the data plate, the max amps at 480 is 30.1. The power factor on the data plate says .8, however the load bank is purely resistive and has a pf of 1.0. So, I put 30.1 amps on it and the generator couldn't take it. My boss told me that I was overloading the generator and that i need to factor in the .8 power factor, but my thinking is--the load is a 1.0 so i need to forego the pf and run it at what the data plate says. Who is right and who is wrong? a little explanation of pf would be helpful. thanks.

matt
 
Engineering news on Phys.org
He is right. Generally in generators we face the two group limitation, mechanical and electrical limitation. In your description you just concentrate to machine electrical characteristics whereas you should check the mechanical performance of machine too.
Seemingly, the active power capacity of your machine is 25/0.8 = 20 KW, if it is right, you can drive a resistive load with maximum current of 24 A (20000/1.73*480) not 30.1 A.



-----------------------------------------------------------------
Creative thinking is enjoyable, Then think about your surrounding things and other thought products. http://electrical-riddles.com
 
Resistive load bank for testing generators

We have developed a resistive load bank 30 KWatts in our setup based on readings we have taken on different loads with different generators and maximum current rating observed was 36 Amperes at 0.8 Pwr Factor. Therefore, we designed our load bank catering to the maximum current being drawn by the load and developed our load bank with a capacity of 45 Amperes (which is 20 % over and above the observed current).

Now, the user is objecting on our design on the premise that we have designed our load bank as purely resistive bank of loads without appreciating the fact that our developed load bank design is already catering the maximum current rating.

Kindly offer your comments whether there are going to be any parameters which will remain un-checked if our load bank is connected to a generator having same specifications (i.e 30 KVA).

Best regards

Adeel
 
Hey guys. I have a question related to electricity and alternating current. Say an alien fictional society developed electricity, and settled on a standard like 73V AC current at 46 Hz. How would appliances be designed, and what impact would the lower frequency and voltage have on transformers, wiring, TVs, computers, LEDs, motors, and heating, assuming the laws of physics and technology are the same as on Earth?
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
I used to be an HVAC technician. One time I had a service call in which there was no power to the thermostat. The thermostat did not have power because the fuse in the air handler was blown. The fuse in the air handler was blown because there was a low voltage short. The rubber coating on one of the thermostat wires was chewed off by a rodent. The exposed metal in the thermostat wire was touching the metal cabinet of the air handler. This was a low voltage short. This low voltage...