Sizing Generator for 10hp Petter Diesel Engine | KVA Alternator

  • Thread starter Thread starter burnit
  • Start date Start date
  • Tags Tags
    Generator Sizing
AI Thread Summary
To size a KVA alternator for a 10hp Petter diesel engine, it's important to consider the engine's power output and efficiency at different RPMs. The engine is rated at 3000 RPM but will produce less power at 2500 RPM, potentially limiting output to around 3000 watts. Running an alternator rated at 15 KVA may lead to inefficiencies if not properly matched to the engine's capabilities. A pulley system could help achieve the desired RPM for optimal performance, but care must be taken to maintain the correct frequency. Proper mounting and torsional vibration issues should also be addressed to ensure reliable operation.
burnit
Messages
52
Reaction score
0
Hi All,

I have a 10hp Petter diesel engine that i want to drive an AC Alternator--Generator 240v AC.

Is there an online calculator for this or can somebody help me size the correct KVA Alternator for it, i want to produce the maximum power i can with this engine to keep it loaded.

Thank You
 
Engineering news on Phys.org
Looking at the specs for a few generators on-line the HP seems to 1.7 to 1.8 x the kVa.

e.g... 8.5hp diesel engine - maximum rated 5.0 kva
 
Pumblechook

Yeah i also noticed online that some 10hp engines had around 5.0 KVA, then some have more & some less?

I need to keep this 10hp engine fully loaded & produce as much power as i can with it.
 
I have found an alternator that is much bigger than required by the engine but it is at a give away price.

If i was to connect this to the 10hp engine & load it just enough for the engine hp would this be ok?
This way i can get a good load on the engine & let it run at the required rpm.

Any problems with this?
 
What speed is your 10hp engine rated at?

How big is the alternator?

Running an alternator at much below its rating decreases efficiency. You may also have problems mounting the engine to the alternator, and with torsional vibration.
 
Hi,

The engine is rated at 3000rpm but i would like to operate it at 2500rpm max for reliabillity.

The Alternator is rated at 15KVA, i get what your saying about the efficiency.

Thanks.
 
You have to run at the correct speed and keep it fairly constant in order to produce the right frequency.
 
Yes your correct, Frequency is something i neglected to think about--good point!

Thank You
 
1 hp = 746 watts. calculate in efficiency and you get the max watts supported by your engine. As far as running it at a lower speed, you can do that with a pulley system to overdrive your generator. In your case 3000/2500 = a 1:1.2 overdrive ratio. Another thing you need to remember is that your engine is rated for 10 Hp at 3000 RPM, It will produce less at 2500 RPM, so be sure to factor this in as well. You may be suprised to learn that you may only be able to power 3000 watts or so.
 