Hiddencamper said:
Power source transfers should be fast. Usually fast transfer logic is tied to the 86 device or a differential fault logic, and I've also seen automatic transfers off of house power to the power grid tied off of main generator breaker positions. Fast transfer logic will synchronize both off site sources for a split second before dumping the faulted bus and prevents a loss of voltage.
Hmm well enough.. makes perfect sense for a normal operation . By 'synchronize' do you mean parallel?
The case above though had a generator lockout... paralleling the onsite and offsite would have backfed the generator zone through the (faulted) aux transformer for duration of that parallel. Our lockout scheme would have blocked that.
Even with a slow transfer, a typical 4160+ voltage switchgear should transfer and close in on the alternate source before the switchgear's undervoltage relay detects it and does a load shed.
Indeed speed is of the essence. Obviously you are well versed, but if anybody else is curious...
Speed up your thinking to millisecond steps. We're going to transfer from onsite to offsite power.
First, onsite feed breaker opens. That disconnects the bus from the onsite power transformer that's (usually) wired straight to the generator.
Bus voltage does not drop to zero because bus has a lot of huge induction motors connected to it. And induction motors will act like induction generators until their internal field dies down which takes a small number of seconds.
However - all those motors do slow down because there's no more energy being put into the bus. So the bus voltage sinewave starts to both get smaller, and slide out of phase with and behind the offsite voltage sinewave.
You cannot close the offsite breaker when there's a large phase difference because excessive currents will flow and wreck something.
So the transfer from onsite to offsite MUST be completed either:
1. BEFORE the bus slows down and gets more than a few degrees behind offsite ,
2. or, AFTER the bus voltage has decayed to near zero
Our plant's switchgear allowed (iirc) 12 line cycles, 1/5 second for that automatic transfer, at end of that time it was blocked by a timer relay.. It actually made the transfer in 5 cycles.
Should transfer fail, diesels would start and restore power in about ten seconds.
Our switchgear had a special "early" aux contact that granted permission for offsite breaker to start closing while onsite breaker was still traveling open. Sort of a "head start", if you will. "GE Magneblast" and it was great stuff in its day...
We had high speed oscillographic recorders on bus voltages , part of post trip analysis was verifying smooth transfers.
Ohhhh nostalgia...
Thanks for your input. You seem to have seen a lot more plants than i.
old jim