The discussion focuses on determining the transient parameters of synchronous machines following a three-phase short circuit. Key points include the significance of the constant 0.368 in calculating time constants and the methods for plotting waveforms. Participants reference IEEE 551/2006 and IEC 60909 standards for calculating short-circuit currents and machine reactances. They discuss the challenges of obtaining necessary data, particularly when manufacturer specifications are unavailable. The conversation highlights the importance of established formulas for calculating time constants based on machine impedance and open-circuit characteristics.
tim9000
Messages
866
Reaction score
17
Hi, So we're doing this Lab on Transient reactance of a synch generator and I'm reading Sarma's classic: Electric Machines Steady-state theory and Dynamic performance p. 474-479

But I can't see how to get the actual exponential time constants for the sub-transient and transient reactances?
Thanks
 
Engineering news on Phys.org
Does the constant 0.368 have any significance? It's almost like he's saying to progress 36.8% from the initial transient peak, then that time is the time constant for the transient?
Also how do you plot the envolope around a waveform?

Lastly, how to you work out the asymmetrical DC component? Fourier or something?
 
http://www.nerc.com/comm/PC/System%20Analysis%20and%20Modeling%20Subcommittee%20SAMS%20DL/Stability%20and%20Modeling%20Workshops/03_Gen_Testing_Related_Topics.pdf

That link shows an overview. There is an IEEE standard for how to perform those tests. I looked for a link to the standard, but failed to find it.

Search for power plant model validation.
 
There are some standards in order to calculate the short-circuit currents.
The most importants ,I think, are IEEE 551/2006 –this is the last edition I know- and IEC 60909.
In IEEE 551/2006 Calculating Short-Circuit Currents in Industrial and Commercial Power Stations the synchronous machine reactance is treated in CH.5 and the short circuit current
at the terminals of this machine [formula 5.1]:
Isc=(E/X”dv-E/X’dv)e^(-t/T”do)+ (E/X’dv-E/Xdv)e^(-t/T’do)+E/xd
Where :
X’’dv=Direct-axis saturated subtransient reactance
X’dv= Direct-axis saturated transient reactance
Xd =synchronous reactance
T’’do=subtransient time constant
T’do= transient time constant
In IEC 60909-2 ch. 2.3 there are Data on typical synchronous machines [Table 2]
 
Babadag said:
There are some standards in order to calculate the short-circuit currents.
The most importants ,I think, are IEEE 551/2006 –this is the last edition I know- and IEC 60909.
In IEEE 551/2006 Calculating Short-Circuit Currents in Industrial and Commercial Power Stations the synchronous machine reactance is treated in CH.5 and the short circuit current
at the terminals of this machine [formula 5.1]:
Isc=(E/X”dv-E/X’dv)e^(-t/T”do)+ (E/X’dv-E/Xdv)e^(-t/T’do)+E/xd
Where :
X’’dv=Direct-axis saturated subtransient reactance
X’dv= Direct-axis saturated transient reactance
Xd =synchronous reactance
T’’do=subtransient time constant
T’do= transient time constant
In IEC 60909-2 ch. 2.3 there are Data on typical synchronous machines [Table 2]
Hi, thanks.
Right, but how do I work out the Direct-axis saturated subtransient reactance, Direct-axis saturated transient reactance, synchronous reactance or the sub or transient, timeconstants?

Thanks
 
Usually there are manufacturer data. Never-the-less in some standards are approximate formulae as for instance:
From IEC 61363-1 ch.6.2.6 Time constants
“If the a.c. and d.c. time constants are unavailable, they can be calculated from the machine
open-circuit time constants and impedance as follows:
Subtransient time constant (usually of the order of 1 ms to 30 ms):
  1. T"d = (X"d / X'd) T"do (32)
  2. Transient time constant (usually of the order of 20 ms to 1200 ms):
    T'd = (X'd / Xd) T'do (33)
    c) d.c. time constant (usually of the order of 15 ms to 300 ms):
    Tdc = X"d /(2.pi.fr.Ra)
 
Babadag said:
Usually there are manufacturer data. Never-the-less in some standards are approximate formulae as for instance:
From IEC 61363-1 ch.6.2.6 Time constants
“If the a.c. and d.c. time constants are unavailable, they can be calculated from the machine
open-circuit time constants and impedance as follows:
Subtransient time constant (usually of the order of 1 ms to 30 ms):
  1. T"d = (X"d / X'd) T"do (32)
  2. Transient time constant (usually of the order of 20 ms to 1200 ms):
    T'd = (X'd / Xd) T'do (33)
    c) d.c. time constant (usually of the order of 15 ms to 300 ms):
    Tdc = X"d /(2.pi.fr.Ra)
Hmm, because I took the current waveform for the field and phases on the CRO using a solid state switch on the zero crossing. So I have the transient oscillations of the current, but no manufacturer data.
 