I don't know the specifics of UL 508 transformer temperature rise testing, but odds are it is similar to the procedures in IEEE 112. It may be I'm underthinking this, but temperature rise ought to be on the transformer nameplate. Let's say it isn't, and measurement is necessary.
srinaath said:
My query is
1) which method is superior and please explain me the reason.
2) Which gives higher value of measurement?
Neither method is universally superior - it still depends on what you are trying to find out.
How do you mean "Which gives a higher value of measurement"? Which technique yields a numerically larger value? Or in the sense of which measurement technique gives results more closely aligned with actual temperature changes?
Broadly speaking, the 'resistance change' technique isn't suitable for determining the maximum temperature rise that occurs after one or more bolted fault trials. Temperature distribution isn't uniform - winding temperature is driven higher deep within the winding because the cooling medium and heat sinking can't get at it. Resistance change gives the average, under-represents this hot spot temperature, and direct measurement may be the only recourse. Problem is, the only way to get a temperature probe to the hot spot is to build it into the winding, and have some foreknowledge of where the hot spot temperature is located.
If you want to learn temperature rise at rated current over a reasonably long period of time then both methods have their pros and cons.
How large is the transformer in question? It is difficult to answer to your questions otherwise.
Thermal time constant is larger for large transformers than it is for small ones. Pulse transformers in an SCR gating application are tiny, and (unless an IR sensor is used to measure core temperature) whatever temperature probe is applied will be a significant fraction of the transformer's mass, act as a heat sink, and affect the measurement. By the same token, it doesn't take very long for such a small mass to cool off, and resistance must be measured immediately after the pulse generator is turned off. These things aren't as much of an issue, for instance, in a 50 kVA dry transformer.