In an extra high voltage substation, a protection system with main and backup distance protection, sync/auto reclosing relays, and CBF protection sometimes fails to operate correctly during severe short circuits. Despite the line distance protection and CBF relay functioning properly, all circuit breakers connected to a bus bar may trip without bus bar protection activation. Investigations suggest that transient pulses from the short circuit could inadvertently trigger other breakers. Additionally, subsidence current from current transformers can prolong the assertion of the breaker failure relay, leading to false operations in tightly coordinated systems. Enhanced digital protective relays are now capable of detecting this subsidence current to mitigate such issues.
m.s.j
Messages
212
Reaction score
1
In an extra high voltage substation, the output overhead lines protected by standard protection system.
That protection system contains high quality main and backup distance protection, sync/auto reclosing relays and separated static relay that specified to line circuit breaker which is named "CBF protection".
The CBF protective relay has connected in series to same current transformer core that connected to distance relay. Also because the extra high voltage power system stability requirements, the relays setting have done in tightly coordination systems. But the designed protection system sometimes couldn't operate correctly.
Sometimes all circuit breakers that connected to one of two substation bus bar (double bus bar system) are tripped due to one sever short circuit that occurred in one of output lines without any bus bar protection activity.
According to more investigation and data recording analyses, the line distance protection had operated correctly (less than 30 ms) and it had opened relevant circuit breaker in time. Also the CBF protective relay had operated too.

How can you explain the reason of that protection system mol operation?


REGARDS
MSJ

----------------------------------------------------------------------
Creative thinking is enjoyable,Then think about your surrounding things and other thought products. http://electrical-riddles.com
 
Engineering news on Phys.org
"Sometimes all circuit breakers that connected to one of two substation bus bar (double bus bar system) are tripped due to one sever short circuit that occurred in one of output lines without any bus bar protection activity."
I am not sure I follow totally but couldn't this sever short cause a transit pulse to trip the other breakers?
 
dlgoff said:
I am not sure I follow totally but couldn't this sever short cause a transit pulse to trip the other breakers?

For drawing and CBF logic diagram refer to attached file.

BEST REGARDS
MSJ
 

Attachments

  • 12.GIF
    12.GIF
    4 KB · Views: 535
Is existence of CT secondary current possible without any its primary current?
Yes it is possible in transient duty. That current named decay or subsidence current.
The subsidence current is the current that flows through a CT burden after the line breaker opens.
As you know, the circuit breaker failure over current relay (50BF) should be fast pickup and dropout relay. The subsidence current may affect the dropout time of breaker failure over current element. If the 50BF element is picked up the breaker failure time delay, other breakers must trip to isolate the failed breaker.
CT subsidence current keep the 50BF element asserted longer than necessary and may contribute to a false breaker failure operation in tightly coordinated systems.
Nowadays some digital base protective relays are able to detect CT subsidence current.


BEST REGARDS
MSJ


-----------------------------------------------------
Creative thinking is enjoyable,Then think about your surrounding things and other thought products. http://electrical-riddles.com
 
Very basic question. Consider a 3-terminal device with terminals say A,B,C. Kirchhoff Current Law (KCL) and Kirchhoff Voltage Law (KVL) establish two relationships between the 3 currents entering the terminals and the 3 terminal's voltage pairs respectively. So we have 2 equations in 6 unknowns. To proceed further we need two more (independent) equations in order to solve the circuit the 3-terminal device is connected to (basically one treats such a device as an unbalanced two-port...
Thread 'Weird near-field phenomenon I get in my EM simulation'
I recently made a basic simulation of wire antennas and I am not sure if the near field in my simulation is modeled correctly. One of the things that worry me is the fact that sometimes I see in my simulation "movements" in the near field that seems to be faster than the speed of wave propagation I defined (the speed of light in the simulation). Specifically I see "nodes" of low amplitude in the E field that are quickly "emitted" from the antenna and then slow down as they approach the far...
Back
Top