Three phase AC concepts and problems

Click For Summary
SUMMARY

The discussion focuses on calculating the total complex power, power factor, and supply current for three loads connected in parallel across a 12.47 kV three-phase supply. Load 1 is an inductive load of 60 kW and 660 kvar, Load 2 is a capacitive load of 240 kW at a 0.8 power factor, and Load 3 is a resistive load of 60 kW. The total complex power is determined to be 360 kW + j480 kVAR, resulting in a power factor of 0.6. Additionally, a Y-connected capacitor bank is proposed to improve the overall power factor to 0.8 lagging, requiring a total of 70 kVAR and a capacitance of 3.6 μF per phase.

PREREQUISITES
  • Understanding of three-phase AC systems
  • Knowledge of complex power calculations
  • Familiarity with power factor correction techniques
  • Proficiency in using phasor representation for AC circuits
NEXT STEPS
  • Study the calculation of complex power in three-phase systems
  • Learn about power factor correction using capacitor banks
  • Explore the implications of Y-connected and Δ-connected loads
  • Investigate the use of phasor diagrams in AC circuit analysis
USEFUL FOR

Electrical engineers, power system analysts, and students studying three-phase AC circuit design and power factor correction techniques will benefit from this discussion.

PainterGuy
Messages
938
Reaction score
73
Hi

Problem:
Three loads are connected in parallel across a 12.47 kV three-phase supply.
Load 1: Inductive load, 60 kW and 660 kvar.
Load 2: Capacitive load, 240 kW at 0.8 power factor.
Load 3: Resistive load of 60 kW.
(a) Find the total complex power, power factor, and the supply current.
(b) A Y-connected capacitor bank is connected in parallel with the loads.
Find the total kvar and the capacitance per phase in μF to improve the overall
power factor to 0.8 lagging. What is the new line current?

Attempt at the solution:
Please have a look here, or the code below which might some formatting errors.

Three loads
are connected in parallel across a 12.47 kV three-phase supply.Load 1: Inductive load, 60 kW and 660 kvar.Load
2: Capacitive load, 240 kW at 0.8 power factor.Load 3: Resistive load of 60 kW.(a) Find the total complex
power, power factor, and the supply current.(b) A Y-connected capacitor bank is connected in parallel with the loads.

Find the total kvar and the capacitance per phase in ##\mu##F to improve the overallpower factor to 0.8 lagging. What is
the new line current?Load 1: ##\mathbf{S}_{l o a d 1} =60 k +j 660 k##Load 2: Using Power Factor ## =\frac{P}{S} =\cos (\theta _{v} -\theta _{i}) \Longrightarrow S =\frac{P}{\cos (\theta _{v} -\theta _{i})} =\frac{240 k}{0.8} =300 k## ;##S =\vert \mathbf{S}\vert =\sqrt[{2}]{P^{2} +\vert Q\vert ^{2}} \Longrightarrow \vert Q\vert =\sqrt[{2}]{S^{2} -P^{2}} =\sqrt[{2}]{300 k^{2} -240 k^{2}} =180 k####\mathbf{S}_{l o a d 2} =240 k -j 180 k##Load 3: ##\mathbf{S}_{l o a d 3} =60 k +j 0####\mathbf{S}_{t o t a l} =\left (60 k +j 660 k\right ) +\left (240 k -j 180 k\right ) +60 k =360 k +j 480 k##Using ##S =\vert \mathbf{S}\vert =\sqrt[{2}]{P^{2} +\vert Q\vert ^{2}}## \qquad and\qquad Power Factor ## =\frac{P}{S} =\cos (\theta _{v} -\theta _{i})####S =\vert \mathbf{S}\vert =\sqrt[{2}]{P^{2} +\vert Q\vert ^{2}}## ## =\sqrt[{2}]{360 k^{2} +\vert 480 k\vert ^{2}} =600 k####\frac{P}{S} =\cos (\theta _{v} -\theta _{i}) \Longrightarrow \cos (\theta _{v} -\theta _{i}) =\frac{360 k}{600 k} =0.6##Assuming ##12.47## ##k V## as RMS line voltage of wye-connected source.Using##V_{L} =\sqrt[{2}]{3} V_{p}## where ##V_{L} =V_{a b} =V_{b c} =V_{b c}## and ##V_{p} =V_{a n} =V_{b n} =V_{c n}##Also the line voltages lead their corresponding phase voltages by ##30 \mbox{{\ensuremath{{}^\circ}}}##, i.e.##\mathbf{V}_{L} =\left (\sqrt[{2}]{3} V_{p}\right )\angle \left (\theta _{V_{p}} +30 \mbox{{\ensuremath{{}^\circ}}}\right )#### \Longrightarrow V_{p} =V_{a n} =\frac{V_{L}}{\sqrt[{2}]{3}} =\frac{12.47 k}{\sqrt[{2}]{3}} =7.2## ##k V##hence ##\mathbf{V}_{a n} =7.2 k \angle 0 \mbox{{\ensuremath{{}^\circ}}}####\mathbf{S}_{t o t a l} =360 k +j 480 k## which means total power supplied is ##360## ##k W## and ##480## ##k V A R##by all three phases of the source therefore power supplied by one phaseof the source
is ##120 k +j 160 k##.Using ##\mathbf{S} =\mathbf{V}_{r m s} \mathbf{I}_{r m s}^{ \ast }####\mathbf{S} =\mathbf{V}_{r m s} \mathbf{I}_{r m s}^{ \ast } \Longrightarrow \mathbf{I}_{r m s}^{ \ast } =\frac{\mathbf{S}}{\mathbf{V}_{r m s}} =\frac{120 k +j 160 k}{7.2 k \angle 0 \mbox{{\ensuremath{{}^\circ}}}} =27.78 \angle 53.13 \mbox{{\ensuremath{{}^\circ}}}#### \Longrightarrow \mathbf{I}_{r m s} =27.78 \angle -53.13 \mbox{{\ensuremath{{}^\circ}}}##(b)Per phase power supplied by the source is ##120 k +j 160 k####\cos (\theta _{v} -\theta _{i}) =0.6#### \Longrightarrow \theta _{1} =53.13 \mbox{{\ensuremath{{}^\circ}}}####\theta _{2} =\cos ^{ -1} (0.8) =36.9 \mbox{{\ensuremath{{}^\circ}}}####\theta _{1}## is the original power factor angle and ##\theta _{2}## is the desired angle. Likewise, ##Q_{1}##is the original reactive power and ##Q_{2}## is the desired reactive power at ##\theta _{2}##.##Q_{i n j e c t e d} =Q_{1} -Q_{2} =P (\tan \theta _{1} -\tan \theta _{2}) =120 k (\tan 53.13 \mbox{{\ensuremath{{}^\circ}}} -\tan 36.9 \mbox{{\ensuremath{{}^\circ}}}) =70## ##k V A R##Original per phase power supplied by the source is ##120 k +j 160 k##After addition of capacitor power supplied is##\left (120 k +j 160 k\right ) +(0 -70 k) =120 k +j 90 k##Using ##C =\frac{Q_{C}}{\omega V r m s^{2}}####C =\frac{Q_{C}}{\omega V r m s^{2}} =\frac{70 k}{2 \pi \times 60 \times 7.2 k^{2}} =3.6## ##\mu F##Using formula \#1:##R =\frac{V_{r m s}^{2}}{P} =\frac{7.2 k^{2}}{120 k} =432## \ \ \ ;
\ \ \ \ ##X =\frac{V_{r m s}^{2}}{Q} =\frac{7.2 k^{2}}{90 k} =576##As power factor is lagging therefore ##\mathbf{Z} =432 +j 576####\mathbf{I}_{a} =\frac{\mathbf{V}_{a n}}{\mathbf{Z}} =\frac{7.2 k \angle 0 \mbox{{\ensuremath{{}^\circ}}}}{432 +j 576} =13.33 \angle -36.9 \mbox{{\ensuremath{{}^\circ}}}##Using different formula \#2:##V_{r m s} I_{r m s}## ##\angle \left (\theta _{v} -\theta _{i}\right ) =P +j Q####7.2 k I_{r m s}## ##\angle \left (0 -\theta _{i}\right ) =120 k +j 90 k#### \Longrightarrow I_{r m s} \angle -\theta _{i} =20.83 \angle 36.87#### \Longrightarrow \mathbf{I}_{a} =20.83 \angle -36.87##

My question:
Although I was able to find the line current in part (b) using formula #2 but am still curious to know that what went wrong with formula #1. I have used it a couple of times in the past to get the correct result. Where am I going wrong? I'm getting wrong Z which in turn leads to wrong value for Ia. I believe that the correct value for Z is 207.52+j207.39. Could you please help me? Thank you!
 
Physics news on Phys.org
Thank you for giving it a look. I have realized that it should have been S=Vrms^2/Z*, and it looks like that formula #1 is a wrong way get Z. Thank you.
 
  • Like
Likes scottdave
PainterGuy said:
Thank you for giving it a look. I have realized that it should have been S=Vrms^2/Z*, and it looks like that formula #1 is a wrong way get Z. Thank you.
OK, good. I had started to look at it, but had not yet figured out enough to post a meaningful response.
 
  • Like
Likes PainterGuy

Similar threads

  • · Replies 9 ·
Replies
9
Views
3K
  • · Replies 7 ·
Replies
7
Views
2K
  • · Replies 11 ·
Replies
11
Views
2K
  • · Replies 33 ·
2
Replies
33
Views
4K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 6 ·
Replies
6
Views
1K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 5 ·
Replies
5
Views
2K
  • · Replies 10 ·
Replies
10
Views
1K