Use of Capacitors for Generators

AI Thread Summary
The discussion centers on improving the power factor of generators, currently at 0.55 and 0.65 for 250 KVA and 365 KVA units, respectively. An Electrical Engineer recommended installing a 90 KVAR Power Capacitor and an Automatic Power Factor Control Panel to achieve a power factor of 0.85. However, another consultant cautioned that larger capacitors could increase the load on alternators, suggesting the use of smaller capacitors at the motor during Delta running instead. The installation of a 15 KVAR capacitor for a 40 HP motor and a 12.5 KVAR capacitor for a 30 HP motor has improved the power factor to 0.72. The discussion seeks guidance on the best capacitor installation approach to ensure the longevity of the generators.
mgSathish
Messages
1
Reaction score
0
When we run our Gensets individually, we are getting a Power Factor of 0.55 and 0.65 for our 250 KVA and 365 KVA Gensets respectively.3. An Electrical Engineer advised us to install a 90 KVAR Power Capacitor and an Automatic Power Factor Control Panel to get a PF of 0.85 for our existing load, to improve the Power Factor when running on Gensets.4. Alternately, another Electrical Consultant advised us that there will be extra load on the Alternators during operation if big Capacitors are installed in the Power Factor Control Panel; rather to use smaller capacitors at the motor, which we will operative only during Delta running of the motors. We have installed a 15 KVAR Capacitor for our 40 HP motor and another 12.5 KVAR Capacitor for our 30 HP motor, only during Delta running. This has improved the Power Factor on our Generators from 0.65 to 0.72.5. We are confused about two opposite views. Please guide us regarding the correct procedure for Capacitor installation, to ensure a long smooth life of our Gensets.
 
Engineering news on Phys.org
I think Consultant 2 is right. Charging capacitors can lead to rather high currents, so it´s advisable to use smaller ones close to the loads.
 
  • Like
Likes mgSathish
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...
Back
Top