Homework Statement


In the circuit below the batteries have negligible internal resistance and the voltmeter V has a very high resistance. What would be the reading of the voltmeter?

ccd53ec942ce.jpg


Answer: 9.6 V.

2. The attempt at a solution
I used the Kirchhoff's rule: the current that flows from 10 V is I1, current that flows to the voltmeter is (I1 - I3) and the current that flows into the 8 V is I3. So I got 10 - 8 = 4 I3 + 1 I1 and 10 = RV (I1 - I3) + 1 I1. But this doesn't look like it can be solved. We have R which I don't what to do with it. Any ideas please?
 
Physics news on Phys.org
The voltmeter has a high resistance (ideally infinite resistance) so it passes no current. What does that tell you about the relationship between ##I_1## and ##I_3##?
 
  • Like
Likes   Reactions: moenste
gneill said:
The voltmeter has a high resistance (ideally infinite resistance) so it passes no current. What does that tell you about the relationship between ##I_1## and ##I_3##?
That I1 - I3 = 0?

I also calculated: I = V / R = 10 / 1 = 10 A and so V1 = 10 * 1 = 10 V and I = 8 / 4 = 2 A, so V2 = 8 V.
 
moenste said:
That I1 - I3 = 0?
Sure, or in other words, ##I_1 = I_3##. So there's really only one current:
upload_2016-9-30_8-44-46.png

I also calculated: I = V / R = 10 / 1 = 10 A and so V1 = 10 * 1 = 10 V and I = 8 / 4 = 2 A, so V2 = 8 V.
No, you need to take the entire loop into consideration in order to determine the current. Write KVL around the loop and solve for the current.
 
  • Like
Likes   Reactions: moenste
gneill said:
Sure, or in other words, ##I_1 = I_3##. So there's really only one current:
View attachment 106742

No, you need to take the entire loop into consideration in order to determine the current. Write KVL around the loop and solve for the current.
Don't we get 10 - 8 = 4 * I + 1 * I → 2 = 5 * I → I = 0.4 A?
 
moenste said:
Don't we get 10 - 8 = 4 * I + 1 * I → 2 = 5 * I → I = 0.4 A?
Looks good.
 
  • Like
Likes   Reactions: moenste
gneill said:
Looks good.
And then we have V = I R + 0.4 * 1 = 0.4 V or 0.4 * 4 = 1.6 V. And then either 10 - 0.4 = 9.6 V or 8 + 1.6 = 9.6 V. Should be correct.