VSD output is erratic in no load test only.

  • Thread starter Thread starter ahendawy85
  • Start date Start date
  • Tags Tags
    Load Output Test
AI Thread Summary
The discussion revolves around a field service engineer's issues with a Variable Speed Drive (VSD) controlling a three-phase induction motor, particularly during no-load tests where the second phase outputs lower voltage. Despite static checks showing all components intact, the V phase displays erratic readings and DC voltage presence at the output. Suggestions include potential diode failure under load, timing issues, and the possibility of a winding-to-winding fault in the transformer. Observations indicate that the VSD may require a small load to stabilize voltage outputs, and the presence of DC voltage in the output raises concerns about the drive's performance. The engineer is encouraged to conduct further tests, including checking transformer windings and using appropriate measurement tools to diagnose the issue effectively.
ahendawy85
Messages
1
Reaction score
0
Hi all, I have a problem with a VSD at work that's been confusing.
I am a field service engineer for an oil service company, my line of work is in electric submersible pumps (ESP). The ESP motor is a 3 phase induction motor. Power here is 380V 50 HZ.We were using a VSD for motor control. The control scheme used by this VSD is constant V/HZ.
When performing a no load test the 2nd phase outputted a lower voltage than the other two.
For example when operating the VSD in no load at 50 HZ output frequency, measuring the output terminal phase to phase yields these readings:
U-V 270VAC
V-W 270VAC
U-W 380VAC
Obviously the V phase has a problem so I disconnect power and start doing some static checks on the VSD. I check the converter's SCR's and the inverter's IGBT's they all check out according to the VSD manual. Measured the DC bus and it does have the correct DC voltage value.
The confusing part is when I connected a small motor to the VSD and started testing it it checked out fine, readings are all balanced and the motor runs smoothly.
U-V 370VAC
V-W 380VAC
U-W 379VAC
Tried a no load test after and same thing happened, the V phase is giving erratic readings. And one last observation; the V phase has DC volts in it, when measuring with my AVO meter for DC volts at the output I get those readings:
U-V 80 VDC
V-W 80 VDC
U-W OL

I'm sorry if it took too long to explain, I just can't seem to find the problem. According to my static test results all components are intact. Any thoughts?
 
Engineering news on Phys.org
I'm guessing that your "no load test" actually draws more current then your "small motor test". If so (and I hope I'm not teaching my grandmother to suck eggs here) it looks as if one of the diodes that carries actual current is failing under load. Sorry if that's too basic but without schematics I'm only guessing.
 
if the parts are all good your symptom suggests timing.
but the DC suggests a winding-to-winding fault in transformer

is this drive the same make as your others? I O W is this unusual for that type VSD?

Perhaps it needs a small load to pull the voltages into phase -
imagine in your mind a star phasor diagram
three arrows pointing out from center 120 degrees apart
... if they re-arranged themselves into a tee instead of a star, eg 90 deg apart instead of 120, V would be closer to U and W than it should

but i can't get past the DC in output, that sounds suspicious

you said static checks
one failure mode for SCR's is "transistoring" where they act as a transistor instead of a switch so don't stay on after the gate pulse ends. Therefore in your static check you have to apply enough current to latch the scr, usually 50 ma or less but still several ma, and a dmm won't do that you need an old timey analog on RX1 . A Simpson 260 never let me down... but even it won't latch big SCR's.

good luck - I'm curious about this one keep us posted...
is there a neutral on this thing?
If phase to neutral voltages are okay but phase to phase unbalanced then you KNOW it's timing.

i'd lift leads and check that transformer for winding to winding short,,,,
then swap SCR's from another unit...
then swap SCR firing board

scratching my head with you... especialy about that DC component
i guess the motor shorts out the DC, so it must be coming through some substantial impedance else something would get real hot.

also- some true RMS voltmeters will correctly calculate the DC component of an offset AC waveform like you describe. That could complicate your observations, so check your DMM manual.


old jim
 
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...