What are load calculations for a transformer?

AI Thread Summary
Load calculations for a transformer involve determining the maximum current based on its kVA rating and the voltage supplied. For instance, a 3750 kVA transformer on a 44 kV line results in a primary current of approximately 49.2 amps per phase. The distribution of load among transformers depends on their rated power and impedance voltage. Understanding these calculations is crucial for effective transformer operation and load management. For further details, resources like Transformer Riddle No. 27 can be consulted.
shaibaaz3
Messages
2
Reaction score
0
what are load calculations for a transformer?

A 44kv line is distributed into the industry using around 8 transformers 3750kva, 2500kva and 1500kva. What does this mean and what are the load calculations for this? Also how is it distributed?
 
Engineering news on Phys.org


KVA is simply volts times amps. And, it's usually three-phase, so you divide the line-to-line voltage by the square root of 3 to find the line-neutral voltage. So, for example, if you have 44 kV into a 3750 kVA transformer, the maximum current will be 3750 / (44 / SQRT (3)) / 3 = 49.2 amps per phase primary current.
 


thank u...
 


Distribution of load on individual transformers is related to their rated power and impedance voltage. For detail calculation you can refer to Transformer Riddle No. 27 from http://electrical-riddles.com
 
Last edited:
Hey guys. I have a question related to electricity and alternating current. Say an alien fictional society developed electricity, and settled on a standard like 73V AC current at 46 Hz. How would appliances be designed, and what impact would the lower frequency and voltage have on transformers, wiring, TVs, computers, LEDs, motors, and heating, assuming the laws of physics and technology are the same as on Earth?
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
I used to be an HVAC technician. One time I had a service call in which there was no power to the thermostat. The thermostat did not have power because the fuse in the air handler was blown. The fuse in the air handler was blown because there was a low voltage short. The rubber coating on one of the thermostat wires was chewed off by a rodent. The exposed metal in the thermostat wire was touching the metal cabinet of the air handler. This was a low voltage short. This low voltage...
Back