What Gauge Wire Should Be Used for the Neutral in a 240VAC Circuit?

Click For Summary
SUMMARY

The appropriate gauge for the neutral wire in a 240VAC circuit supplied by a transformer and protected by a 20A circuit breaker should be 10AWG, based on NEC guidelines. The neutral must be sized to handle the maximum unbalanced current, which is calculated using a 140% multiplier for a 3-wire, single-phase system. This means that for a 20A load, the neutral can experience up to 28A, necessitating the use of 10AWG wire. Additionally, all conductors should be of the same gauge to ensure safety and compliance with electrical standards.

PREREQUISITES
  • Understanding of NEC (National Electrical Code) regulations
  • Knowledge of wire gauge sizing and current capacity
  • Familiarity with single-phase and multi-phase electrical systems
  • Basic electrical safety practices
NEXT STEPS
  • Research NEC Section 220-22 for neutral sizing requirements
  • Learn about the differences between single-phase and two-phase systems
  • Study the implications of using 140% multipliers in electrical calculations
  • Explore best practices for selecting wire gauge for various electrical loads
USEFUL FOR

Electricians, electrical engineers, and anyone involved in residential wiring or electrical system design will benefit from this discussion, particularly those working with 240VAC circuits and NEC compliance.

PEMFC
Messages
3
Reaction score
0
A transformer supplies 240VAC to a 20A circuit breaker as shown in the attached image. I believe I can use 12AWG wire for wires X1, X4, 2 & 3. However, I'm not sure what gauge wire the neutral should be. Maybe 12AWG or something larger?
 

Attachments

Engineering news on Phys.org
PEMFC said:
A transformer supplies 240VAC to a 20A circuit breaker as shown in the attached image. I believe I can use 12AWG wire for wires X1, X4, 2 & 3. However, I'm not sure what gauge wire the neutral should be. Maybe 12AWG or something larger?
Welcome to PhysicsForums.

What does the NEC say? If you don't know what the NEC is, what does your electrician say? :wink:
 
PEMFC said:
However, I'm not sure what gauge wire the neutral should be. Maybe 12AWG or something larger?
A 240V device drawing current from the two outer terminals will not have a neutral current.

However, when both 120V circuits are being operated with the shared neutral, since they are of opposite phase, the currents returning from the two actives will not sum but will partly cancel in the neutral.

For that reason I would expect all conductors to be of the same gauge appropriate to the 20 amp breaker.
 
  • Like
Likes   Reactions: PEMFC
Yes. Absolute worst case is simply using one side.
 
  • Like
Likes   Reactions: PEMFC and DaveE
Even if you have a 240 volt only load with no 120 volt loads, you have to size what you are calling the neutral large enough to carry maximum fault current. You have the center tap grounded at the transformer, so you have to have a safety ground and this is what you are calling the neutral. If you have 120 volt loads as well, you need a fourth conductor.
 
240 volt at 20 amp is 4800 VA.
So why is the transformer only rated for 3000 VA ?
 
  • Like
Likes   Reactions: PEMFC
The NEC says the Neutral must be not smaller than the supply conductors.
(I don't have my copy handy at the moment, someone borrowed it and it is overdue. :cry:)

Cheers,
Tom
 
  • Like
Likes   Reactions: PEMFC
Averagesupernova said:
Even if you have a 240 volt only load with no 120 volt loads, you have to size what you are calling the neutral large enough to carry maximum fault current. You have the center tap grounded at the transformer, so you have to have a safety ground and this is what you are calling the neutral. If you have 120 volt loads as well, you need a fourth conductor.
At least in the US, conductor #1 is indeed referred to as the neutral. The safety ground is a fourth conductor, not shown, connected to the case or frame of the equipment being powered but not intended to supply power.
 
I did find a website that apparently references the NEC:

“Sizing the neutral: Sec. 220-22. You must size the neutral conductor to carry the maximum unbalanced current in the circuit (i.e. the largest load between the neutral and anyone ungrounded phase conductor)...”

The website also says:

“You must use a multiplier of 140% when calculating the neutral current for a 3-wire, 2-phase or 5-wire, 2-phase system.”

So, for this scenario it would appear that the maximum load between the neutral and a phase conductor is limited to 20A by the circuit breaker. Also, this appears to be a 3-wire, 2-phase system, so my guess is that 20A x 140% = 28A so 10AWG wire for the neutral is probably the best bet.

Baluncore, you are correct, it does appear that either the Transformer is too small or the Circuit Breaker needs to be reduced.
 
  • #10
PEMFC said:
Also, this appears to be a 3-wire, 2-phase system, so my guess is that 20A x 140% = 28A so 10AWG wire for the neutral is probably the best bet.
No. It is NOT 2-phase.
 
  • Like
Likes   Reactions: CalcNerd
  • #11
sandy stone said:
At least in the US, conductor #1 is indeed referred to as the neutral. The safety ground is a fourth conductor, not shown,
Based on the diagram I don't know how you can say it is one or the other. They are not the same by definition but the diagram makes no attempt to label.
 
  • #12
Averagesupernova said:
No. It is NOT 2-phase.
Ok, I see. It’s a Single-Phase, 3-wire system. Thanks.
 
  • #13
Averagesupernova said:
Based on the diagram I don't know how you can say it is one or the other. They are not the same by definition but the diagram makes no attempt to label.
I see your point. From a US-centric perspective, that is a diagram of a residential supply, and I thought there could have been safety issues regarding nomenclature.
 
  • #14
Nomenclature: Power in the US is typically called split phase power which comes from a center tapped transformer with local ground. Two phase power has one quadrature (##\pi/2## out) signal and so is not symmetric under time reversal.
 
  • Like
  • Informative
Likes   Reactions: Tom.G and Averagesupernova

Similar threads

  • · Replies 42 ·
2
Replies
42
Views
4K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 16 ·
Replies
16
Views
5K
  • · Replies 32 ·
2
Replies
32
Views
4K
  • · Replies 10 ·
Replies
10
Views
4K
  • · Replies 4 ·
Replies
4
Views
3K
  • · Replies 18 ·
Replies
18
Views
8K
  • · Replies 6 ·
Replies
6
Views
5K
Replies
7
Views
7K
Replies
3
Views
5K