What Gauge Wire Should Be Used for the Neutral in a 240VAC Circuit?

Click For Summary

Discussion Overview

The discussion revolves around the appropriate gauge wire to use for the neutral in a 240VAC circuit, particularly in the context of a 20A circuit breaker. Participants explore various aspects of electrical wiring, including safety considerations, code requirements, and the implications of different load types.

Discussion Character

  • Technical explanation
  • Debate/contested
  • Conceptual clarification

Main Points Raised

  • Some participants suggest using 12AWG wire for the neutral, while others propose that it should be larger to accommodate potential fault currents.
  • It is noted that a 240V device drawing current from two outer terminals will not have neutral current, but when both 120V circuits are used, the neutral current may vary due to phase cancellation.
  • One participant emphasizes that the neutral must be sized to carry maximum fault current, especially since the center tap is grounded at the transformer.
  • Another participant references the NEC, stating that the neutral must not be smaller than the supply conductors and mentions a specific sizing rule for unbalanced loads.
  • There is a discussion about the transformer rating being potentially inadequate for the load, raising questions about the circuit breaker size.
  • Some participants clarify the system type, correcting earlier claims about it being a 2-phase system to a single-phase, 3-wire system.
  • Concerns are raised regarding the nomenclature used in the diagram, with some participants unsure about the labeling of conductors.

Areas of Agreement / Disagreement

Participants express differing views on the appropriate gauge for the neutral wire, with no consensus reached on whether 12AWG or a larger gauge is necessary. There is also disagreement regarding the classification of the electrical system as either 2-phase or single-phase.

Contextual Notes

Participants reference the NEC for guidance on wire sizing, but there are uncertainties regarding specific interpretations and applications of the code. The discussion also highlights the importance of understanding the implications of load types on neutral sizing.

Who May Find This Useful

Individuals interested in electrical engineering, residential wiring, or those seeking clarification on NEC guidelines may find this discussion relevant.

PEMFC
Messages
3
Reaction score
0
A transformer supplies 240VAC to a 20A circuit breaker as shown in the attached image. I believe I can use 12AWG wire for wires X1, X4, 2 & 3. However, I'm not sure what gauge wire the neutral should be. Maybe 12AWG or something larger?
 

Attachments

Engineering news on Phys.org
PEMFC said:
A transformer supplies 240VAC to a 20A circuit breaker as shown in the attached image. I believe I can use 12AWG wire for wires X1, X4, 2 & 3. However, I'm not sure what gauge wire the neutral should be. Maybe 12AWG or something larger?
Welcome to PhysicsForums.

What does the NEC say? If you don't know what the NEC is, what does your electrician say? :wink:
 
PEMFC said:
However, I'm not sure what gauge wire the neutral should be. Maybe 12AWG or something larger?
A 240V device drawing current from the two outer terminals will not have a neutral current.

However, when both 120V circuits are being operated with the shared neutral, since they are of opposite phase, the currents returning from the two actives will not sum but will partly cancel in the neutral.

For that reason I would expect all conductors to be of the same gauge appropriate to the 20 amp breaker.
 
  • Like
Likes   Reactions: PEMFC
Yes. Absolute worst case is simply using one side.
 
  • Like
Likes   Reactions: PEMFC and DaveE
Even if you have a 240 volt only load with no 120 volt loads, you have to size what you are calling the neutral large enough to carry maximum fault current. You have the center tap grounded at the transformer, so you have to have a safety ground and this is what you are calling the neutral. If you have 120 volt loads as well, you need a fourth conductor.
 
240 volt at 20 amp is 4800 VA.
So why is the transformer only rated for 3000 VA ?
 
  • Like
Likes   Reactions: PEMFC
The NEC says the Neutral must be not smaller than the supply conductors.
(I don't have my copy handy at the moment, someone borrowed it and it is overdue. :cry:)

Cheers,
Tom
 
  • Like
Likes   Reactions: PEMFC
Averagesupernova said:
Even if you have a 240 volt only load with no 120 volt loads, you have to size what you are calling the neutral large enough to carry maximum fault current. You have the center tap grounded at the transformer, so you have to have a safety ground and this is what you are calling the neutral. If you have 120 volt loads as well, you need a fourth conductor.
At least in the US, conductor #1 is indeed referred to as the neutral. The safety ground is a fourth conductor, not shown, connected to the case or frame of the equipment being powered but not intended to supply power.
 
I did find a website that apparently references the NEC:

“Sizing the neutral: Sec. 220-22. You must size the neutral conductor to carry the maximum unbalanced current in the circuit (i.e. the largest load between the neutral and anyone ungrounded phase conductor)...”

The website also says:

“You must use a multiplier of 140% when calculating the neutral current for a 3-wire, 2-phase or 5-wire, 2-phase system.”

So, for this scenario it would appear that the maximum load between the neutral and a phase conductor is limited to 20A by the circuit breaker. Also, this appears to be a 3-wire, 2-phase system, so my guess is that 20A x 140% = 28A so 10AWG wire for the neutral is probably the best bet.

Baluncore, you are correct, it does appear that either the Transformer is too small or the Circuit Breaker needs to be reduced.
 
  • #10
PEMFC said:
Also, this appears to be a 3-wire, 2-phase system, so my guess is that 20A x 140% = 28A so 10AWG wire for the neutral is probably the best bet.
No. It is NOT 2-phase.
 
  • Like
Likes   Reactions: CalcNerd
  • #11
sandy stone said:
At least in the US, conductor #1 is indeed referred to as the neutral. The safety ground is a fourth conductor, not shown,
Based on the diagram I don't know how you can say it is one or the other. They are not the same by definition but the diagram makes no attempt to label.
 
  • #12
Averagesupernova said:
No. It is NOT 2-phase.
Ok, I see. It’s a Single-Phase, 3-wire system. Thanks.
 
  • #13
Averagesupernova said:
Based on the diagram I don't know how you can say it is one or the other. They are not the same by definition but the diagram makes no attempt to label.
I see your point. From a US-centric perspective, that is a diagram of a residential supply, and I thought there could have been safety issues regarding nomenclature.
 
  • #14
Nomenclature: Power in the US is typically called split phase power which comes from a center tapped transformer with local ground. Two phase power has one quadrature (##\pi/2## out) signal and so is not symmetric under time reversal.
 
  • Like
  • Informative
Likes   Reactions: Tom.G and Averagesupernova

Similar threads

  • · Replies 42 ·
2
Replies
42
Views
4K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 16 ·
Replies
16
Views
5K
  • · Replies 32 ·
2
Replies
32
Views
4K
  • · Replies 10 ·
Replies
10
Views
4K
  • · Replies 4 ·
Replies
4
Views
3K
  • · Replies 18 ·
Replies
18
Views
8K
  • · Replies 6 ·
Replies
6
Views
5K
Replies
7
Views
8K
Replies
3
Views
5K