This is a situation I don't often deal with; I have an underground piping system that is failing a pressure test and losing pressure at a rate of about 1psi/min from 80psi. I'd like to calculate the leakage rate.
The pipe is a simple 10" diameter, schedule 40 steel pipe, 500' long (0.365" th). That's roughly 2,038.8 gal.
First, I calculate the compressibility of water. Googling, I'm seeing 2.8% compression for 1,000 psi (taken from a graph). Or 0.06 gal/psi. This feels reasonable.
Next, I use the hoop stress equation and 29 MPsi Young's Modulus to calculate the expansion of the pipe. I get a volume difference of 0.0019 gal. This feels surprisingly low.
Could someone double-check me please.
The pipe is a simple 10" diameter, schedule 40 steel pipe, 500' long (0.365" th). That's roughly 2,038.8 gal.
First, I calculate the compressibility of water. Googling, I'm seeing 2.8% compression for 1,000 psi (taken from a graph). Or 0.06 gal/psi. This feels reasonable.
Next, I use the hoop stress equation and 29 MPsi Young's Modulus to calculate the expansion of the pipe. I get a volume difference of 0.0019 gal. This feels surprisingly low.
Could someone double-check me please.