The discussion clarifies that PN16, JIS10k, and ANSI 150# have different pressure ratings, with PN16 rated for 16 bar and ANSI 150# being a higher rating. It emphasizes that while JIS10k is comparable in pressure, there are significant differences in valve and flange dimensions. The conversation also highlights the importance of matching valve ratings to the steam pressure in a system, as steam pressure affects temperature. Concerns are raised about using a PN16 globe valve at maximum operating temperatures close to its limit, although it may still be acceptable under certain conditions. Overall, proper engineering practices are crucial when dealing with high-energy systems like boilers.
onestep
Messages
3
Reaction score
0
Hi,

I have a question.

Glove Valve

PN16, JIS10k , ANSI 150#, AMSE, all they equal same, in withstand the steam pressure?

I heard RN16 stand for 16bar pressure, but it's for steam too?

I'm confuse..

million thanks if anyone would teach me please.
 
Engineering news on Phys.org
PN16 is a lower rating than ANSI 150#. JIS10k is basically equivalent as far as pressure rating goes, but there are many differences in the valve/flange dimensional specs. ASME (Specifically ASME B16.5) is the pressure rating specification.

Steam pressure dictates steam temperature. Valves must be rated to the steam pressure that will be in the system.
 
thanks for the answers.. :D

1 more question,

lets say,

The boiler operation temperature are between 150~200 Celsius , and the operation pressure are between around 10 to 12 bar.

With attach a cast iron body globe valve, with PN16, Max temperature 200Celsius. It's suitable?

Thank you.
 
I suppose. I'd be a little suspicious of a valve with a maximum temperature of 200C if your standard operating temp is ~200C, but you'd probably be ok. Boiler engineering isn't something to guess at though, they store a great deal of energy and you don't want to under engineer them.

PN16 is rated to 16 bar, or ~230psi. At your 200C you'll be seeing a max operating pressure of ~175psi which is about 3/4 max rating. That should be ok.
 
ok, got it. Million thanks Travis King. :)
 
Hi all, I have a question. So from the derivation of the Isentropic process relationship PV^gamma = constant, there is a step dW = PdV, which can only be said for quasi-equilibrium (or reversible) processes. As such I believe PV^gamma = constant (and the family of equations) should not be applicable to just adiabatic processes? Ie, it should be applicable only for adiabatic + reversible = isentropic processes? However, I've seen couple of online notes/books, and...
Thread 'How can I find the cleanout for my building drain?'
I am a long distance truck driver, but I recently completed a plumbing program with Stratford Career Institute. In the chapter of my textbook Repairing DWV Systems, the author says that if there is a clog in the building drain, one can clear out the clog by using a snake augur or maybe some other type of tool into the cleanout for the building drain. The author said that the cleanout for the building drain is usually near the stack. I live in a duplex townhouse. Just out of curiosity, I...
I have an engine that uses a dry sump oiling system. The oil collection pan has three AN fittings to use for scavenging. Two of the fittings are approximately on the same level, the third is about 1/2 to 3/4 inch higher than the other two. The system ran for years with no problem using a three stage pump (one pressure and two scavenge stages). The two scavenge stages were connected at times to any two of the three AN fittings on the tank. Recently I tried an upgrade to a four stage pump...
Back
Top