What is the voltage at the service with a 20V drop on a 3ph line of 347/600?

  • Thread starter Thread starter rozilla
  • Start date Start date
  • Tags Tags
    Voltage
AI Thread Summary
In a 3-phase line of 347/600V, a 20V drop can be interpreted differently depending on the reference point. The voltage at the service is typically 580V when considering the three-phase system. The relationship between single-phase and three-phase voltages is clarified by the formula involving the square root of three. A 20V drop in a single-phase scenario equates to a 34.6V drop in a three-phase context, while a 20V drop in a three-phase scenario corresponds to an 11.5V drop in single-phase. Understanding these relationships is crucial for applying voltage drop concepts effectively.
rozilla
Messages
2
Reaction score
0
Hi guys,

If there was a voltage drop of 20V on a 3ph line of 347/600, is the voltage at the service 327V or 580V, or both? Thanks you for reading.

RozilΩ
 
Engineering news on Phys.org
Is this a homework problem? What do YOU think the answer is, and why?
 
Who observed a voltage drop of 20V ?
How did they measure it ?
 
Hi guys,

This isn't school related. That isn't the actual voltage - I'm trying to understand the concept of which would be the operating. With the concept, I can apply it accordingly. I assume it is 580 as it is three phase.
 
The specified voltage is 347V / 600V.
The three phases are separated by 120°. 1 / Tan(30°) = √3 = 1.73205
If you multiply 347V by √3 you get 600V.
You cannot change one without changing the other.

When combined with a common neutral you have three single phase supplies of 347V, relative to the neutral. The voltage between the phases is 600V.

A 20V single phase drop is a 34.6V three phase drop.
A 20V three phase drop is an 11.5V single phase drop.
 
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
Thread 'Electromagnet magnetic field issue'
Hi Guys We are a bunch a mechanical engineers trying to build a simple electromagnet. Our design is based on a very similar magnet. However, our version is about 10 times less magnetic and we are wondering why. Our coil has exactly same length, same number of layers and turns. What is possibly wrong? PIN and bracket are made of iron and are in electrical contact, exactly like the reference design. Any help will be appreciated. Thanks. edit: even same wire diameter and coil was wounded by a...
Thread 'Beauty of old electrical and measuring things, etc.'
Even as a kid, I saw beauty in old devices. That made me want to understand how they worked. I had lots of old things that I keep and now reviving. Old things need to work to see the beauty. Here's what I've done so far. Two views of the gadgets shelves and my small work space: Here's a close up look at the meters, gauges and other measuring things: This is what I think of as surface-mount electrical components and wiring. The components are very old and shows how...
Back
Top