What is the voltage at the service with a 20V drop on a 3ph line of 347/600?

  • Thread starter Thread starter rozilla
  • Start date Start date
  • Tags Tags
    Voltage
AI Thread Summary
In a 3-phase line of 347/600V, a 20V drop can be interpreted differently depending on the reference point. The voltage at the service is typically 580V when considering the three-phase system. The relationship between single-phase and three-phase voltages is clarified by the formula involving the square root of three. A 20V drop in a single-phase scenario equates to a 34.6V drop in a three-phase context, while a 20V drop in a three-phase scenario corresponds to an 11.5V drop in single-phase. Understanding these relationships is crucial for applying voltage drop concepts effectively.
rozilla
Messages
2
Reaction score
0
Hi guys,

If there was a voltage drop of 20V on a 3ph line of 347/600, is the voltage at the service 327V or 580V, or both? Thanks you for reading.

RozilΩ
 
Engineering news on Phys.org
Is this a homework problem? What do YOU think the answer is, and why?
 
Who observed a voltage drop of 20V ?
How did they measure it ?
 
Hi guys,

This isn't school related. That isn't the actual voltage - I'm trying to understand the concept of which would be the operating. With the concept, I can apply it accordingly. I assume it is 580 as it is three phase.
 
The specified voltage is 347V / 600V.
The three phases are separated by 120°. 1 / Tan(30°) = √3 = 1.73205
If you multiply 347V by √3 you get 600V.
You cannot change one without changing the other.

When combined with a common neutral you have three single phase supplies of 347V, relative to the neutral. The voltage between the phases is 600V.

A 20V single phase drop is a 34.6V three phase drop.
A 20V three phase drop is an 11.5V single phase drop.
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...