Which side of a transformer secondary to be ground referenced?

  • Context: Engineering 
  • Thread starter Thread starter musicgold
  • Start date Start date
  • Tags Tags
    Ground Transformer
Click For Summary
SUMMARY

The discussion centers on the grounding of the secondary side of a control transformer, specifically the X1 and X2 terminals. It is established that X2 should be grounded because it serves as the neutral side of the control circuit, ensuring safety and proper operation. Grounding X1 is not advisable as it is connected to a fuse, which could lead to disconnection of the ground if the fuse blows. Proper termination of the low-voltage side of the transformer must follow the manufacturer's instructions to ensure safety and functionality.

PREREQUISITES
  • Understanding of control transformer wiring, specifically X1 and X2 terminals.
  • Knowledge of electrical grounding principles and safety protocols.
  • Familiarity with fuse functions in electrical circuits.
  • Ability to interpret manufacturer schematics for transformer installation.
NEXT STEPS
  • Research the grounding techniques for control transformers in industrial applications.
  • Learn about the implications of grounding different terminals in AC systems.
  • Study the role of fuses in electrical safety and circuit protection.
  • Examine manufacturer guidelines for terminating low-voltage transformer connections.
USEFUL FOR

Electrical engineers, technicians working with control systems, and anyone involved in the installation and maintenance of transformers in industrial settings.

musicgold
Messages
303
Reaction score
19
Homework Statement
Not a homework question. I wish to know how do I decide which side of the secondary of an isolation transformer can be grounded.
Relevant Equations
At the 6.20 mark in the video below, the instructor says that if a system needs grounded pilot voltage, it is common to ground the X2 terminal of the secondary.
The video is located here. My question, if the secondary side is isolated and the control circuit has no connection to the primary side, why do I have to ground X2 only? This a floating AC system, so why does it matter which side is used as the reference? What will happen if I grounded the X1 terminal?
1645417483830.png
 
Physics news on Phys.org
Sorry, I didn't watch the video, but from your schematic, there's no way to decide which side should be grounded. It is an arbitrary choice at this level of detail.
 
Ground the X2 side, because X1 has a fuse.
You do not want a blown fuse to disconnect the ground.
 
  • Like
Likes   Reactions: hutchphd, Tom.G, berkeman and 1 other person
From:

(https://abbott-tech.com/ is a major supplier of both Military and Industrial, harsh environment, power supplies)

Step 6- Terminate the low-voltage side of the transformer following the manufacturer’s instructions and schematics for different types of transformers. For small control transformers, there will be X1 and X2 terminals only where X1 is the power side and X2 the grounding and a side of the low voltage.

Cheers,
Tom
 
And step 7 answers the OP's question.
Step 7- Terminate the control transformer for X1 and X2 where X1 goes straight to control circuit after it passes through a fuse usually rated for the circuit. X2 is terminated to the neutral side of the control circuit and is also used for grounding safety. Therefore, X2 terminal of the small control transformer must be wound together to a grounding structure of the circuit.
 

Similar threads

  • · Replies 7 ·
Replies
7
Views
3K
  • · Replies 2 ·
Replies
2
Views
2K
Replies
6
Views
4K
  • · Replies 1 ·
Replies
1
Views
5K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 17 ·
Replies
17
Views
4K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 6 ·
Replies
6
Views
19K
Replies
14
Views
3K