Why Does Neutral & Ground Short Together in AC Circuits?

  • Thread starter Thread starter monus76
  • Start date Start date
  • Tags Tags
    Ground Neutral
AI Thread Summary
In AC circuits, neutral and ground should only be connected at the main service entrance, not in subpanels or disconnects. Historically, it was permissible to connect neutral and ground in subpanels, but modern standards require separation to ensure safety. The grounding systems defined in IEC 60364, such as TN, TT, and IT, serve to protect against insulation faults and enhance safety. Understanding the specific requirements and resources is crucial for selecting the appropriate grounding system. Proper adherence to these guidelines is essential for the safety of electrical installations.
monus76
Messages
3
Reaction score
0
hi there
need help

i just need to know why ground and neutral ( A.C CIRCUITS) short together on the body of machine chassis or panels.i found this in one oil heating unit ,with high wattage of heating element.

who ever can reply ,highly appreciated

with thanks
 
Engineering news on Phys.org
It depends on when the installation was done. New installations should never have the neutral and ground hooked together except in the main service entrance. Any subpanel, disconnect for a furnace, air conditioner, etc. must keep the neutral and ground seperated. In the past, the neutral and ground were allowed to be shared or connected in subpanels. Search physics forums for this sort of thing. It's been discussed before.
 
In low voltage systems, the three main grounding system are used as defined in IEC 60364:

- Exposed-conductive parts connected to neutral -TN-
- Earthed neutral -TT-
- Unearthed (or impedance-earthed) neutral -IT-

The purpose of these three systems is identical as regards protection of persons and property mastery of insulation fault effects. For choosing the best grounding system, it is important to know our requirements and resources.

For more information you can refer to Grounding riddle No.21 in http://electrical-riddles.com
 
Last edited:
Very basic question. Consider a 3-terminal device with terminals say A,B,C. Kirchhoff Current Law (KCL) and Kirchhoff Voltage Law (KVL) establish two relationships between the 3 currents entering the terminals and the 3 terminal's voltage pairs respectively. So we have 2 equations in 6 unknowns. To proceed further we need two more (independent) equations in order to solve the circuit the 3-terminal device is connected to (basically one treats such a device as an unbalanced two-port...
Thread 'Weird near-field phenomenon I get in my EM simulation'
I recently made a basic simulation of wire antennas and I am not sure if the near field in my simulation is modeled correctly. One of the things that worry me is the fact that sometimes I see in my simulation "movements" in the near field that seems to be faster than the speed of wave propagation I defined (the speed of light in the simulation). Specifically I see "nodes" of low amplitude in the E field that are quickly "emitted" from the antenna and then slow down as they approach the far...