Troubleshooting Strange Noise from 250kw 3 Phase Motor

AI Thread Summary
A new 250kW 3-phase motor wired in delta is producing an intermittent metallic noise resembling spoon tapping, occurring at a frequency of about 1 Hz, while connected to a 170 amp VFD. The motor draws 105 amps at 50 Hz and has been tested without load, showing balanced current across phases. Despite checking for mechanical issues and trying the motor on a different drive without the noise, the problem persists with the original VFD, which sometimes trips on overcurrent without showing a rise in current beforehand. Suggestions include having a professional assess the motor and considering manufacturer support to ensure warranty validity. The stability of the VFD's output voltages and the balanced current readings suggest the issue may lie within the VFD itself.
lottis
Messages
3
Reaction score
0
Hi guys

I have been testing a brand new 250kw 3 motor wired in delta. I have it connected to a 170 amp vfd with no load for testing. It draws 105 amps at 50hz and is balanced.

Intermittently the motor makes a strange that i have not heard before. It sounds like a spoon taping another spoon, a metal on metal sound tapping at no more than 1 hz off and on. When power is removed and the motor free spins to a stop the sound is gone. I have tried different carrier frequency but it does not make any difference.

Sometimes while making the noise the vfd trips on over current but not on output short circuit. The drive does not show a raise in current before tripping.

The motor has been check for mechanical issues, bearing/loose parts etc and none have been found.

I have tried the motor on another drive (250 amp) and it does not make the noise. I have tried other motors (55kw and smaller) on the vfd and they do not make the noise.

Thanks
 
Engineering news on Phys.org
Does it sound like it could be a spark?
 
No not like a spark, a clang but not loud, spoon on spoon is the best description i can think of. When i heard it first i would have sore there was something loose in the motor, like a balance or something, but nothing loose was found.
If these was a short to Earth or across a winding the vsd would either fault "output short" or "earth fault" i would assume.
 
You are saying the motor is balanced? How did this get checked? At 250KW it is worth the investment to get a professional to assess it. ( there are a lot of tests to consider: http://www.motordiagnostics.com/papers/AC%20Motor%20Testing%20and%20Predictive%20Maintenance.pdf )

Also as a new motor - you can ask, or pay for the manufacturer to come check it out, and then have them certify the warranty is intact, it may cost a few $ now - but to ensure the warranty is valid it may be well worth it.

The VFD could be the problem, again at this power level - I would lean on the manufacturer.
 
Last edited by a moderator:
The current is balanced across each phase +/- 2 amps at 105amps 50hz. The vfd shows the current for each phase and i also checked with a clip on ammeter. I also checked winding resistance and insulation resistance which both check out fine.
The dc bus is stable and the vfd output voltages are also stable and balanced.
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...