Averagesupernova
Science Advisor
Gold Member
- 4,851
- 1,520
Ok russ, I will try to explain myself. Starting with 120 volts in either split phase system or the 208 volt system where there is 120 volts from each hot wire to ground. For the sake of my argument the voltage we stick with, for apples to apples comparisons, is 120 volts. As I explained, sharing the neutral in the split phase system eliminates current in one conductor. Actually it eliminates the current in 2 conductors if we split the neutral up and had 2 separate 120 volt feeds. You and I will certainly agree with this am I correct? Some folks will say screw the neutral and just use 240 volts for everything. Yes this is an option and as I have pointed out in another thread which is linked to in this thread doing that has its disadvantages. So, sticking with 120 volts, you cannot eliminate the neutral. In my water heater example I said you can and of course we both agree that is the case. But simply using the phrase split phase it implies 120 volt loads will exist. Otherwise there is no reason for the center tap on the transformer. So, that is my position and I think we can put that part of the discussion to bed.
-
Sophie, I will try to address your points.
-
Concerning what you call 3 phase 240 volt wye system in the UK. I assume that it is 240 volts between neutral and each hot conductor with 415 volts between each hot conductor. We have the same thing in the US except the voltage is halved and we DON'T SPEC THE LOW VOLTAGE. Doing so seems insane to me from a safety perspective. We call it 208 volt wye. I don't think it is possible to get wire in this country rated for less than 600 volts that is used in construction so as jim hardy said it is a moot point.
-
It boils down to this: 3 phase in any configuration and split phase take advantage of using currents that cancel and reduce the loss and wire size in some neutral wires. If you don't see this as an advantage over single phase then at this point I am not sure I can get the point across, although I am sure I will try. :)
-
Sophie, I will try to address your points.
So it is your position that halving the current going to 240 volts is not relevant? I don't recall that being your position in other threads here on PF. 1000 watts may not be much going from one voltage to the other but what about a central air or heat pump unit? Last one I wired was a in small house for what is typically built nowadays and the breaker size spec'd was 25 amp 240 volt double pole breaker. Want to run that on 120 volts? Now you have a 50 amp breaker with much heavier wire.Split phase system (two extremes):
1. Totally balanced = 240V into a 1kW load (= 4.166A)
2. Totally unbalanced = 120V into 1kW load ( = 8.33A)
Doubling the volts uses half the current. I really can't see that's very relevant.
-
Concerning what you call 3 phase 240 volt wye system in the UK. I assume that it is 240 volts between neutral and each hot conductor with 415 volts between each hot conductor. We have the same thing in the US except the voltage is halved and we DON'T SPEC THE LOW VOLTAGE. Doing so seems insane to me from a safety perspective. We call it 208 volt wye. I don't think it is possible to get wire in this country rated for less than 600 volts that is used in construction so as jim hardy said it is a moot point.
-
It boils down to this: 3 phase in any configuration and split phase take advantage of using currents that cancel and reduce the loss and wire size in some neutral wires. If you don't see this as an advantage over single phase then at this point I am not sure I can get the point across, although I am sure I will try. :)