Air pressure difference between floor & ceiling

AI Thread Summary
The discussion revolves around measuring the air pressure difference between the floor and an 8-foot high ceiling using digital manometers. Users report difficulties in obtaining a reading, consistently getting 0 IWC despite expectations of a measurable pressure difference. It is clarified that the air pressure in a vertical hose varies with height, affecting readings, and that using a flexible hose can introduce inaccuracies due to wall deformation. For accurate measurements, it is suggested to use an instrument that measures absolute pressure rather than relative pressure. The conversation highlights the importance of understanding how pressure behaves in a vertical column of air and the limitations of certain measurement setups.
tinkeringone
Messages
15
Reaction score
0
Can't figure out how to get my digital manometers to read the pressure difference between the air near the floor vs. at the 8' high ceiling. It reads 0 IWC no matter how I do it. One of my instruments is a micromanometer (reads as low as .001 IWC pressure differential), and it reads 0 IWC there too.
I'm zeroing the meter at floor level, and have no hose on the "reference" port. And I gave a 9 foot manometer hose on the "signal" port with the meter at floor level and the open end of the hose a few feet from the ceiling.
I'm thinking that there be about a 0.108 IWC PD there with that 8' difference in height. Why am I getting 0? It isn't an air tight room, and no fans are on.
 
Engineering news on Phys.org
Are you accounting for the air pressure in the manometer tube...?
 
russ_watters said:
Are you accounting for the air pressure in the manometer tube...?

I guess not, if the tube you're referring to is the hose going from the digital manometer to the ceiling. I assumed that pressure in the hose was the same as the air pressure at the ceiling where the open end of that hose is.
Never had to do that just measuring static pressure, i.e. in an air duct. But I guess that was at about the same height as the meter.
How would I account for the pressure in that hose?
 
tinkeringone said:
I assumed that pressure in the hose was the same as the air pressure at the ceiling where the open end of that hose is.

No. The air pressure in a vertical length of hose will vary with height, exactly the same way as the air pressure in the room.

If you position the hose vertically, seal the end, and then bring it down to floor level you should see a difference in reading. But correcting the reading to give you an accurate measurement would be complcated, especially if the hose is flexible.

The straightforward way to measure this is with an instrument that measures absolute pressure, not relative, and is sensitive enough to show the small pressure difference.
 
Thank you, AZ, as I too was unsuccessfully "measuring" height air dP in my room with a diff. manometer. Now I see why - so simple. I have tried just now, and exactly, as you imply, it is not possible with a flexible hose as a slightest deformation of its walls causes huge pressure fluctuations.
 
Posted June 2024 - 15 years after starting this class. I have learned a whole lot. To get to the short course on making your stock car, late model, hobby stock E-mod handle, look at the index below. Read all posts on Roll Center, Jacking effect and Why does car drive straight to the wall when I gas it? Also read You really have two race cars. This will cover 90% of problems you have. Simply put, the car pushes going in and is loose coming out. You do not have enuff downforce on the right...
I'm trying to decide what size and type of galvanized steel I need for 2 cantilever extensions. The cantilever is 5 ft. The space between the two cantilever arms is a 17 ft Gap the center 7 ft of the 17 ft Gap we'll need to Bear approximately 17,000 lb spread evenly from the front of the cantilever to the back of the cantilever over 5 ft. I will put support beams across these cantilever arms to support the load evenly
Thread 'What's the most likely cause for this carbon seal crack?'
We have a molded carbon graphite seal that is used in an inline axial piston, variable displacement hydraulic pump. One of our customers reported that, when using the “A” parts in the past, they only needed to replace them due to normal wear. However, after switching to our parts, the replacement cycle seems to be much shorter due to “broken” or “cracked” failures. This issue was identified after hydraulic fluid leakage was observed. According to their records, the same problem has occurred...
Back
Top