Balance between generated and consumed power

  • Thread starter Thread starter bd411
  • Start date Start date
  • Tags Tags
    Balance Power
AI Thread Summary
In an AC electricity system, when a large generator is disconnected, the balance between generated and consumed power is disrupted, leading to a decrease in frequency. If demand exceeds generation, the load exerts torque on the rotor, causing the frequency to drop, similar to Lenz's law. The governors of the remaining generators play a crucial role in maintaining frequency by adjusting output to match demand, ensuring stability within the system. They switch generators in and out to keep the frequency close to its nominal value, typically around 50Hz in the UK. Understanding this dynamic is essential for preventing system-wide failures.
bd411
Messages
39
Reaction score
0

Homework Statement



Consider an AC electricity system operating with a balance between generated power and the consumed power. Explain what happens to the frequency of a system if a large generator is suddenly disconnected. Explain the role of the governors of the remaining generators in controlling the frequency.

Homework Equations



N/A


The Attempt at a Solution



Hello all :)

I am having some trouble understanding the relationship between generated power, consumed power and frequency of the system.

I understand that when generation exceeds demand the excess energy builds up in the inertia of the generators and the frequency rises. I'm looking for the oppositely equivalent statement, i.e. "when demand exceeds generation...".

My best guess at a solution is that when demand exceeds generated power, it exerts some sort of torque on the rotor in the opposite direction to its inertia and therefore decreases the frequency ? Kind of like Lenz's law ?

As for the second part of the question, it is the role of the governors to switch in and out generators in order to keep the frequency at its nominal value, which is 50hz +/- 1% in the UK. This ensures there is a very low possibility of a system wide collapse.

Any help with this would be very greatly appreciated. Thank you in advance.
 
Physics news on Phys.org
Think of each power plant as an engine (eg diesel or steam) that turns a generator at 50 or 60 revolutions per second (depending on your country). If you increase the load on the generator that will increase the load on the engine causing it to slow down. If the engine slows down the rpm of the generator will slow and so will the frequency of the grid.

Edit: It's not really correct to think of this in terms of inertia although clearly the rotating machinery does have inertia.
 
Last edited:
Thanks a a lot for your reply, it's made it much easier to visualise what's going on :)
 