A 30-volt loss in power supply can contribute to an electric motor overheating, especially if the motor is operating near its maximum current draw. The motor's insulation class may allow for higher temperatures, but inadequate ventilation or external heat sources could exacerbate the issue. It's essential to ensure that the generator's output matches the motor's frequency and specifications. Increasing the generator's voltage may not resolve the overheating if the underlying issues, such as mechanical load or ventilation, are not addressed. Further readings and checks on the motor's specifications are recommended to diagnose the problem accurately.
Joe P
Messages
2
Reaction score
0
Hello, looking for some information on electric motor theory for a problem I encountered on a friends machine. An on site generator is our power supply, our motor requires 480v/ac 3phase, our generator is providing 500v/ac but we are losing 30 volts under load from our extension leads. our motor is running very hot but not tripping overload relays. My question is - could the 30 volt loss of power cause this problem. Also if I increase the voltage output on my generator will it solve the problem. Thanks joe
 
Engineering news on Phys.org
Without knowing how the overload relays are sized, the mechanical load and current drawn by the motor vs. the nameplate max current it is hard to recommend anything. Accepting 30 volts of loss in the wiring is not exactly good practice even if it does put the voltage at the motor right where you want it. Also, 'very hot' is a relative term. It can depend on if the motor is ventilated in the way that the designers intended.
 
Is it possible the motor has a problem? If so, maybe that's where the 30 volt drop is coming from.
 
Presuming the overload protection is suitable set on then the current it is in its correct limits. Elevated voltage could raise the no-load current-this could be checked of course. Usually the rated voltage is 460 V so 500 V [if this is the measured voltage at motor terminals] but 8.7% more it is not so elevated voltage.
The motor could be “very hot” if the insulation permits this. Insulation class H permits a conductor temperature of 180 dgr.C and 70-80 dgr.C outside stator surface could be permissible.
However the overload protection does not “protect” the motor against a defective ventilation or if a heat source in vicinity may deliver a substantial heat –even sunshine or else.
 
Joe P said:
our motor is running very hot but not tripping overload relays.

Hi Joe P. http://img96.imageshack.us/img96/5725/red5e5etimes5e5e45e5e25.gif

Check that the generator is matched to the motor's frequency, e.g., both 60Hz.
 
Last edited by a moderator:
Thank you for the the helpful info, We are going to take more readings and check the motor tag specifications,
Thanks all Joe
 
Thread 'Weird near-field phenomenon I get in my EM simulation'
I recently made a basic simulation of wire antennas and I am not sure if the near field in my simulation is modeled correctly. One of the things that worry me is the fact that sometimes I see in my simulation "movements" in the near field that seems to be faster than the speed of wave propagation I defined (the speed of light in the simulation). Specifically I see "nodes" of low amplitude in the E field that are quickly "emitted" from the antenna and then slow down as they approach the far...
Hello dear reader, a brief introduction: Some 4 years ago someone started developing health related issues, apparently due to exposure to RF & ELF related frequencies and/or fields (Magnetic). This is currently becoming known as EHS. (Electromagnetic hypersensitivity is a claimed sensitivity to electromagnetic fields, to which adverse symptoms are attributed.) She experiences a deep burning sensation throughout her entire body, leaving her in pain and exhausted after a pulse has occurred...